RE the backfed to dusk till dawn -- isn't that also the case with the 2 PIR sensors and the manual switch?
They are backfed, but as their inputs are always live, this is a normal situation, their own electronics remain powered by the input. What is abnormal about the sensor is that it can be backfed when the input is dead (due to the timer being off), so if it is active when the timer goes off, the electronics start being powered from the output instead of the input.
If the sensor output is switched by a relay, there won't be any problem; it simply won't notice that the supply for its own electronics is coming in via the output as the relay makes a solid connection. It will go off and stay off once the source of the backfeed itself goes off, and no-one will be any the wiser. If its output is switched by a triac, then it might perhaps object to as the load won't be sufficient to hold the triac on properly, possibly making it go wobbly or cycle on and off while it shuts down. Unlikely though, and probably harmless.
Had the timer been controlling anything else independently, then the backfeed could cause a mis-operation, as it would bypass the timer if both controlled devices were active at once.