RE the backfed to dusk till dawn -- isn't that also the case with the 2 PIR sensors and the manual switch?

They are backfed, but as their inputs are always live, this is a normal situation, their own electronics remain powered by the input. What is abnormal about the sensor is that it can be backfed when the input is dead (due to the timer being off), so if it is active when the timer goes off, the electronics start being powered from the output instead of the input.

If the sensor output is switched by a relay, there won't be any problem; it simply won't notice that the supply for its own electronics is coming in via the output as the relay makes a solid connection. It will go off and stay off once the source of the backfeed itself goes off, and no-one will be any the wiser. If its output is switched by a triac, then it might perhaps object to as the load won't be sufficient to hold the triac on properly, possibly making it go wobbly or cycle on and off while it shuts down. Unlikely though, and probably harmless.

Had the timer been controlling anything else independently, then the backfeed could cause a mis-operation, as it would bypass the timer if both controlled devices were active at once.
 
They are backfed, but as their inputs are always live, this is a normal situation, their own electronics remain powered by the input. What is abnormal about the sensor is that it can be backfed when the input is dead (due to the timer being off), so if it is active when the timer goes off, the electronics start being powered from the output instead of the input.

If the sensor output is switched by a relay, there won't be any problem; it simply won't notice that the supply for its own electronics is coming in via the output as the relay makes a solid connection. It will go off and stay off once the source of the backfeed itself goes off, and no-one will be any the wiser. If its output is switched by a triac, then it might perhaps object to as the load won't be sufficient to hold the triac on properly, possibly making it go wobbly or cycle on and off while it shuts down. Unlikely though, and probably harmless.

Had the timer been controlling anything else independently, then the backfeed could cause a mis-operation, as it would bypass the timer if both controlled devices were active at once.
Got it -- what could be done to work around that issue in this case (I know it is probably overkill, but am interested in options regardless)
 
sorry - it wasn't very clear.

The diagram was looking good until you added a house

Send us a picture of the junction box when it is done
It will look just like his diagram, with less straight lines ;)

What is abnormal about the sensor is that it can be backfed when the input is dead (due to the timer being off)

It shouldn't be backfeeding the sensor, it only backfeeds the switch part of the circuit
 
You might want to go through the logic of a timer switch before a dawn-dusk switch; the timer seems superfluous to me.

To avoid running cables to PIR sensors and override switch you could use these wirelessly connected devices to a receiver switch:

EasySwitch Easy Switch Wireless Switches - https://www.tlc-direct.co.uk/Main_Index/Pumps_and_Aquatics_Index/EasySwitch/index.html#EasySwitch

The use of the wireless receiver switch would allow the use of fobs which folk could carry or be left in the car and could obviate the need for the override switch. If you still wanted a separate override switch there is fixed wireless switch which would suit.

Are you bothered about animals or on windy nights swaying trees setting off the PIR for the lighting - it could become annoying.

You might want to think also about beam cutting or retro reflective sensor switches eg:

Takex PR-11B 15m Reflector Beam Sensor - https://connectec.uk/security/intruder-alarms/perimeter-detection/takex-pr-11b-15m-reflector-beam-sensor?gclid=Cj0KCQiAuefvBRDXARIsAFEOQ9GDzyPYfHUOqPWb_5qbAd42I19Gnw5kjYKs1ci9rJVFhd55uzDUvBQaAs_rEALw_wcB
 
Last edited:

Reply to Please check my logic for upgrade lights project wiring! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
628
Hi there, I have an outside light that is turned on with a switch from inside and would like to change it to a PIR version incorporating an...
Replies
8
Views
1K
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
603
Hi, I have ran a light ring off a fused spur with two lights on, each with their own switch (outside and lobby light) I want to put the outside...
Replies
4
Views
2K
Hello all, I know this is very simple but I would like some advice please. I am installing a new circuit to feed 5 external floodlights. It is...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock