Hello

I’ve been carrying out an EICR today and have come across a problem. The property is a small upstairs flat.

I’ve carried out dead tests which all came back good.. no problem on IR. There is some ‘green goo’ present in some switches but it all meggers fine.

The lighting is on a 6A 61009 rcbo 30ma serving 9 points.. including 12v fan.
It is a TNCS system and I have a ZE of 0.21.

When I tried to carry out ZS at a pendant the rcbo trips within about 2 seconds of the test starting. I then try to do an auto rcd test which won’t trip at 1 times. I’ve replaced the rcbo for a new one and still no joy. I’ve tried doing each test seperatly at 1x and 5x but it’s not tripping at all. The functional test on the rcbo works as it should.

I can’t seem to see what the problem could be? Has anyone come across anything like this before? Any help would be great as I am returning tomorrow to finish.
 

Reply to RCBO not tripping on RCD test in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock