Rcd issue head scratcher

Discuss Rcd issue head scratcher in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
25
Hi all. Ive been testing a flat with a main switch consumer unit and a mixture of mcbs and rcbos.

All test perfect until rcd test for kitchen ring rcbo its a wylex b32a rcbo.

With cables connected to rcbo but nothing plugged in it gives readings of >300 for x1 and >40 for x5
Then when cables disconnected the readings are fine. 2 other rcbos in board and they are fine. Tried two other rcbos and same problem occurs. Has anyone came accross this before?
Thanks
 
Possible crossed rings / bridged circuits. The IR might test fine on its own but there's a parallel path back to the board when one of the other circuits is also energised.
 
Hi all. Ive been testing a flat with a main switch consumer unit and a mixture of mcbs and rcbos.

All test perfect until rcd test for kitchen ring rcbo its a wylex b32a rcbo.

With cables connected to rcbo but nothing plugged in it gives readings of >300 for x1 and >40 for x5
Then when cables disconnected the readings are fine. 2 other rcbos in board and they are fine. Tried two other rcbos and same problem occurs. Has anyone came accross this before?
Thanks
Guess there is something wrong with the circuit connected to the RCBO then, answer the circuit needs a complete electrical test.
 

Reply to Rcd issue head scratcher in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock