Is there a Type B solution that incorporates time delay or am I missing something obvious about the operation of different types of RCCB?
Not that I have seen. Doepke have a good range of type B (at a price!) but none are delay ones to mk knowledge.
Sorry if this is a stupid question, but I can't get enough of threads that raise issues specific to TT earthing systems.
No, it is a perfectly sensible question to ask!
 
Types of rcd in series
Images courtesy of BEAMA
 

Attachments

  • 2989CEBA-B5CC-4637-BE7D-E8DBE36B365A.jpeg
    436.9 KB · Views: 31
Last edited:
Some EV manufacturers like Garo particularly stipulate this requirement, that a type AC cannot be upfront of their type A etc.
If also rcd manufacturers are telling you the same thing then that’s good enough for me.
 
Last edited:
Types of rcd in series

That states that no Type S RCCB should be fitted upstream of a Type B or F, which obviously removes any issue of selectivity.

Would this be appropriate for a TT earthing system, given that disconnection may rely on electronics at a single point?
 
That states that no time delayed RCCB should be fitted upstream of a Type B or F, which obviously removes any issue of selectivity.

Would this be appropriate for a TT earthing system, given that disconnection may rely on electronics at a single point?
Not sure I follow?
 
Types of rcd in series
Images courtesy of BEAMA
In your picture Ian, it shows a type A RCD upstream from a type B RCD. It then says a type A RCD should not be upstream from a type B RCD. I'm a little confused?

edit... No it doesn't! My error.

Although It does look like it is suggesting no upfront S type RCD if there is a type B RCD downstream (as there are no S type type B RCD's)
 
It doesn’t, the paragraph above is for S types, the one below is for general rcd selection

My mistake, I was fixated by the diagram.

What I've been driving at is the fact that this discussion has highlighted that operation of Type S RCCBs may be impacted by DC earth leakage from devices that require protection of a Type B RCBO. As such I'm wondering if an upfront Type S RCCB could be rendered ineffective in such circumstances and, if so, what the most appropriate solution might be.
 
My mistake, I was fixated by the diagram.

What I've been driving at is the fact that this discussion has highlighted that operation of Type S RCCBs may be impacted by DC earth leakage from devices that require protection of a Type B RCBO. As such I'm wondering if an upfront Type S RCCB could be rendered ineffective in such circumstances and, if so, what the most appropriate solution might be.
Higher rated type B RCD. E.g 300mA Type B? I can't imagine fitting one though!
 

Reply to RCD requirements for TT? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock