Search the forum,

Discuss RCD tripping at 6ma on ramp in the DIY Electrical Advice area at ElectriciansForums.net

S

Sq-Pants

Hello,
I am a diyer doing my own board change shortly (paying a premium for the honour to BC) and have a problem either with my tester or something else. Basically when i test the RCDs and the two RCBOs i have on the board they are tripping on ramp at crazy figures, 6ma on one RCD and 9ma on the other the RCBO's also trip at 6ma, now i bought these a few weeks ago and they were fine then as i tested them but when i was showing my inquisitive son today they were performing like this, on the first RCD i tested it failed on ramp i then tested again and it passed then tested again and it failed and fails every time since. I then tested an RCD spur i have that was fine when tested a month ago and the same happened on ramp. Every RCD i test on x0.5, x1, & x5 is fine it's just ramp.

So is my tester (KT63) knackered or could there be something else affecting the results?
 
Welcome to the forum Sq-Pants...

Has your test meter been calibrated?

Regarding the ramp test - why are you doing a ramp test as this does not show you what the rcd trips at it merely shows you how many mA the meter added to the circuit before the device operated, its additional to leakage already on the circuit, this is a diagnostic test normally used with nuisance tripping, if the correct rcbo,rcd trip tests are compliant with the BS7671 then I wouldn't worry too much.
 
Last edited:
try ramp testing with the outgoing cables dissed from the RCD/RCBO
 
When you say you're testing these RCDs I assume the tests are being carried out on the circuits , I suggest you test these RCDs at the outgoing terminals of the RCDs with all circuits disconnected from them , sounds like theres leakage on the circuits that could either be appliance or wiring based ..you could initially try the tests again with all appliances unplugged and other equipment isolated...
 
Sq-Pants... Your profile says in training, are you on an Electrical course at the moment?

If so you may be interested in the Trainee section where we have selected mentors and fellow trainee's to help with the expected level of question someone just starting out would ask, its not a requirement to apply and join but it woud be more suited to yourself if you are on a course than asking questions in the main forum :)
 
Thanks for the quick replies
In reply to the posts

Yep MFT is only 3 months old bought as new with end of line cert
I know a ramp test is not required to demonstrate that the RCD is functioning but i did think that i would be wanting it to trip at not less than 15ma to avoid tripping when in use due to normal earth leakage say from the cooker for example, that was my thinking anyway.
Outgoing cables are disconnected and i am testing on the load side of the device (test probes directly on screws).
RCBOs not fed from RCD, line is direct from main switch via busbar and Neutral is on same block as incoming, Rcd 1 is on block 2 and RCD2 on block 3.
Sorry Darkwood i do need to change my profile i was to start training last year but had to abandon it due to lack of money to see me through an apprenticeship, basically i could not afford to leave my current job.
 

Reply to RCD tripping at 6ma on ramp in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
516
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Replies
12
Views
1K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
406
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock