Search the forum,

Discuss Recessed consumer unit in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
5
Hi guys

A customer wants a new surface mounted consumer unit installed. Their current unit is recessed. The cables are not long enough to come out into rear of new board.
Any suggestions would be great. 👍
 
That’s what I was alluding to, rather than just floating connector strip in the void.

I’d there a possibility of using the old recessed board as an enclosure? Fitting a din rail and having a row of din rail connectors? You can get din rail adaptors for holding WAGOs I believe.
That’s not a bad idea. Thanks a lot littlespark. 👍
 
Good suggestion there @littlespark
You can of course get Wago DIN mounted connectors for just this purpose, and pre-populated enclosures too. There's a snag with the CPC ones all being connected to the rail, however you can simply use plain ones for the cpc. Additionally, there are "carriers" that simply allow the normal Wago 221 types to be mounted onto a DIN rail. They are quite neat and not expensive.
Depending on the circuits, you might need beefier versions for a shower or cooker, obviously.
 

Reply to Recessed consumer unit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good morning guys Was looking for advice with regards to installing an outdoor consumer unit. Customer is looking for power to be installed from...
Replies
31
Views
833
Client has had a meter installed for a new consumer unit in their shop they are looking to rent out the spare space for a barber shop so they want...
Replies
10
Views
502
Hey everyone, working on a new build house and outside garage is wired up like this, however customer wants a Garage Consumer Unit instead of the...
Replies
8
Views
380
Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
809

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock