how would I work out the size of capacitor I need to reverse a single phase motor.
Not sure of the size etc as not been out to see it yet all I know is the customer has a fan they want to reverse its in a machine so don't think a fan controller would suit.
 
if you can get at the terminals of the windings, reverse the start winding.
 
You can reverse either the start winding wires or the run winding wires, either option will give you reverse running, just don't reverse both windings.
 
Hi

some motors are marked z1 & z2 these are the start windings and just need to swap them over, if no markings measure the resistance on the 2 sets of windings and the higher of the two will be the start.

Hope this helps

regards
gary
 
If you can't get at the windings as they are sometimes inside the motor, you could always take the impellor off and refit it the opposite way around.
 

Reply to reverse a single phase AC motor in the Electricians' Talk | All Countries area at ElectriciansForums.net

Similar Threads

Hi I have inherited a compressor with a single phase motor but its been stripped and I need to fathom out what's what.. I don't know if it even...
Replies
13
Views
702
Hi, I am looking for a connection diagram or sugestions for a 2.2Kw single phase motor to drive a compressor. The spec plate shows that it can be...
Replies
5
Views
826
Hello Everyone -- So, I am looking to buy a used 5HP 3PH 208 V 10 inch Table saw --- (Motor Plate Data in Image) I am a DIY'er and in...
Replies
2
Views
571
Hello right off the bat I'm a novice with a little better understanding than most(father was a electrician) but I am not an electrician. I'm...
Replies
26
Views
2K
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock