Currently reading:
reverse polarity on appliance socket

Discuss reverse polarity on appliance socket in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
92
Carried out an eicr and noticed x2 double sockets have reverse polarity that supply a frying machine at high level.
After correcting the reverse polarity on the two sockets i plugged the fryer back in and the circuit MCB tripped out and the appliance popped.

I am unable to open the fryer up as its fixed into the unit.

I cant seem to work out why the original appliances required the sockets to have incorrect polarity at the socket, and after correcting the reverse polarity the appliance tripped the fuse.

I checked the newly configured polarity and the sockets were correctly wired wheres before the L-N had been reversed.
 
Last edited:
Carried out an eicr and noticed x2 double sockets have reverse polarity that supply a frying machine at high level.
After correcting the reverse polarity on the two sockets i plugged the fryer back in and the circuit tripped out and the appliance popped.

I cant seem to work out why the original appliances required the sockets to have incorrect polarity at the socket, and after correcting the reverse polarity the appliance tripped the fuse.

I checked the newly configured polarity and the sockets were correctly wired wheres before the L-N had been reversed.
What tripped CB,RCBO or RCD what instrument did you use to confirm correct polarity? looks like you need to carry out some more test on the circuit supplying the 2 twin sockets
 
Without the fryer plugged in the MCB stays on, i checked the plug top and it was fine.
Fault on the fryer then, diagnosing from afar. As the job was an EICR thats, an inspection of the fixed wiring, which you have found and rectified a fault, your client needs to get the fryer tested under ISITEE the new way of saying PATesting, in my opinion.
 
As per Westy, if the circuit is not RCD protected, there is likely an L/E fault in the fryer that was hidden, maybe deliberately, by the reverse polarity at the socket. An IR test or visual will probably find it in minutes, could be within an element. If an RCD is present, it is mildly surprising that this did not trip but doesn't change anything.
 
I don't think archy was implying to bodge it now I think he meant why hadn't the person installing the fryers bodged it that way instead of going to the trouble of doing it at the socket outlets.
Ah OK, sorry Archy, never meant to imply you were a bodger,:(:D:) in any stretch of the imagination.
 
Last edited:

Reply to reverse polarity on appliance socket in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock