Just a quick question from a new qualified sparky.

So in 433.1.204 when it says the Iz of the cable must not be less than 20A for a ring final circuit.
Does this include a radial fused spur taken off the ring final?

If you install it in 2.5mm in trunking then the Iz is immediately down to 20A even before you add in any other factors. (I will be installing this in trunking with a 1.5mm lighting cable, so it will be less)

Will I have to install using a 4mm cable, or seeing as the spurred part of the circuit is protected by a 13a fuse, does that then comply with 433.1.1? (Treat it as a radial, not a ring from that point on?)
 
Last edited:
if you're fitting a 13A FCU, your 1.5mm spur will be compliant. fit as many sockets as you want (within reason).
Thanks Telectrix, I think you got back to me 1st the last time I asked a question...and it was the most helpful answer!

The spurs going to be in 2.5mm, but it's sharing the trunking with a separate light circuit.
I was thinking it would be close with the correction factors and 4mm seemed a bit OTT!

Sadly they only want one socket, but it's all practice!

Thanks again.
 
Just a quick question from a new qualified sparky.

So in 433.1.204 when it says the Iz of the cable must not be less than 20A for a ring final circuit.
Does this include a radial fused spur taken off the ring final?

If you install it in 2.5mm in trunking then the Iz is immediately down to 20A even before you add in any other factors. (I will be installing this in trunking with a 1.5mm lighting cable, so it will be less)

Will I have to install using a 4mm cable, or seeing as the spurred part of the circuit is protected by a 13a fuse, does that then comply with 433.1.1? (Treat it as a radial, not a ring from that point on?)
Hi Steve. How are you getting 20A Iz for 2.5mm in trunking? Should be 23A, ref method B.

As @telectrix says, 1.5mm will generally comply for a fused spur from a ring. Have a look at P505 in your regs book and reference it with chapter 7 OSG for more info.
 
If you install it in 2.5mm in trunking then the Iz is immediately down to 20A even before you add in any other factors. (I will be installing this in trunking with a 1.5mm lighting cable, so it will be less)

If you look at page 409 of the BBB then it states '(enclosed in conduit in an insulated wall)' which is Method A for 20A
As @Pretty Mouth has said, should be 23A.

Also if you look at Note 9 of Table 4C1 it states 'If, due to known operating conditions, a cable is expected to carry not more than 30 % of its grouped rating, it may be ignored for the purpose of obtaining the rating factor for the rest of the group.'
 
Hi Steve. How are you getting 20A Iz for 2.5mm in trunking? Should be 23A, ref method B.

As @telectrix says, 1.5mm will generally comply for a fused spur from a ring. Have a look at P505 in your regs book and reference it with chapter 7 OSG for more info
Yes, you're completely right. I was looking at Ref Method A. I think I've been at this too long without a break!

I was running it in 2.5mm T&E as it was going to run through a wall and back entry into an outside socket for the garden.

I can't believe I was looking at page 505 earlier too.

Many thanks for your help. Glad I'm getting this right now at the design stage rather than having to go back and change something!

Where did you find the ref meth B for T&E, can't find it the regs or OSG?
 
If you look at page 409 of the BBB then it states '(enclosed in conduit in an insulated wall)' which is Method A for 20A
As @Pretty Mouth has said, should be 23A.

Also if you look at Note 9 of Table 4C1 it states 'If, due to known operating conditions, a cable is expected to carry not more than 30 % of its grouped rating, it may be ignored for the purpose of obtaining the rating factor for the rest of the group.'
Yes I must have seen conduit and jumped to conclusions, I was looking at Ref Meth A.

Well that makes it a lot more achievable! I was even considering thermosetting for a moment.

Great tip about 4C1 too, I'm going to do my cable calculations tomorrow now (got caught up on this!) so I'll prove that too.

I want to do this job as thoroughly as possible as its going to be a back up to get registered.

Thanks for the advice, Spoon (and everyone else!), much appreciated!
 

Reply to Ring Fused Spurs and overload protection (433.1.204) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
811
Hi there I am struggling with the following calculation. 4mm Ring Final Circuit, In = 32A Cg - group of 6 with a correction factor of 0.57 Ci -...
Replies
10
Views
2K
Evening all, Been to a job on Fri where the customer had a condition report completed. Two of the remedial identified was that there were too...
Replies
7
Views
1K
Hi, I have a book on domestic wiring which says that everywhere there is a change in current carrying capacity along a circuit there must be some...
Replies
3
Views
336
Hi, quick question. How do FCU's work? Do they just protect the load side and what I mean is, say you have a ring final with 2.5mm^2 protected by...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock