Yes, you're completely right. I was looking at Ref Method A. I think I've been at this too long without a break!

I was running it in 2.5mm T&E as it was going to run through a wall and back entry into an outside socket for the garden.

I can't believe I was looking at page 505 earlier too.

Many thanks for your help. Glad I'm getting this right now at the design stage rather than having to go back and change something!

Where did you find the ref meth B for T&E, can't find it the regs or OSG?
P158 of the OSG, or table 4D2A p403 BBB. It's the table for multicore cables.
 
See what the other guys think, but i normally fit a dp switch inside to completely isolate, but with a SFCU, they have the option to extend from that one socket to another
I hadn't thought about a DP isolator. Originally they were going to put power out to a small summer house, so would have done, but they changed their minds. (Shame i was looking forward to putting an earth rod in!)
I can put one in if necessary and a switched FCU would be better for future proofing, good idea.
Thanks again!
 
Cable grouping derating sometimes needs a bit of common sense factored in. An almost unloaded cable, such as a lighting feed with only a couple of lights further on probably takes heat from your loaded power cable, actually increasing its load capacity if anything, rather than decreasing it.
 
you won'tfind a ref. method B for T/E in conduit as the regs were written assuming that conduit was used only for singles.
 
Cable grouping derating sometimes needs a bit of common sense factored in. An almost unloaded cable, such as a lighting feed with only a couple of lights further on probably takes heat from your loaded power cable, actually increasing its load capacity if anything, rather than decreasing it.
Brian. Glad to see you have had a change of heart about the role "common sense" can play in electrics ?
 
Cable grouping derating sometimes needs a bit of common sense factored in. An almost unloaded cable, such as a lighting feed with only a couple of lights further on probably takes heat from your loaded power cable, actually increasing its load capacity if anything, rather than decreasing it.
I like your comment by the way. And fully agree that there are other factors which can influence decreasing or increasing cable carrying capacity. For instance the Op is talking about installing trunking in his garage rather than indoors in the utility or kitchen. A garage could well be 10 to 15 degrees cooler than indoors which has a direct impact on cable rating.Its like comparing an insulated attic to an uninsulated one.
 

Reply to Ring Fused Spurs and overload protection (433.1.204) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
813
Hi there I am struggling with the following calculation. 4mm Ring Final Circuit, In = 32A Cg - group of 6 with a correction factor of 0.57 Ci -...
Replies
10
Views
2K
Evening all, Been to a job on Fri where the customer had a condition report completed. Two of the remedial identified was that there were too...
Replies
7
Views
1K
Hi, I have a book on domestic wiring which says that everywhere there is a change in current carrying capacity along a circuit there must be some...
Replies
3
Views
336
Hi, quick question. How do FCU's work? Do they just protect the load side and what I mean is, say you have a ring final with 2.5mm^2 protected by...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock