Hi all,

Recently carried out my AM2 exam but failed on safe isolation (single circuits) & fault finding.

The weird thing is I only failed one out of 3 on the safe isolation so not sure what I done differently. I’ve got my Resit booked and just wanted to ensure that I’d be doing it the correct way:
Identify circuit
Ask permission to de-energize circuit
Isolate circuit
Lock off circuit
Apply warning notices
Prove testing equipment
Go to e.g. light fitting and test for any voltage
Re-prove testing equipment
Good to start work.

Does this look all good to you? Originally I took the board cover off but I think it’ll be better to just test the loads (lights, DOL etc)
 
Hi all,

Recently carried out my AM2 exam but failed on safe isolation (single circuits) & fault finding.

The weird thing is I only failed one out of 3 on the safe isolation so not sure what I done differently. I’ve got my Resit booked and just wanted to ensure that I’d be doing it the correct way:
Identify circuit
Ask permission to de-energize circuit
Isolate circuit
Lock off circuit
Apply warning notices
Prove testing equipment
Go to e.g. light fitting and test for any voltage
Re-prove testing equipment
Good to start work.

Does this look all good to you? Originally I took the board cover off but I think it’ll be better to just test the loads (lights, DOL etc)
You passed AM2? If Yes please help my because I have the same situation
 
There is a "Safe Isolation Pocket guide" produced by NICEIC and ELECSA, plus guidance note 3 from the electrical safety council, you shouldn't go wrong if you adhere to those publications should you?
 
Did you put the cover back on the board when you went to test the circuit eg light fitting?
[automerge]1571425538[/automerge]
Does section C take the cover from DB or not?
[/QUOTE]

Good afternoon, i recently failed my fault finding and have the same question... Do you take the cover off? Whats the process? Do i isolate the Main switch or leave that on and just isolate the circuit that i need to find the fault on?

Any help would be greatly apreciate
 
[automerge]1571425538[/automerge]
Does section C take the cover from DB or not?

Good afternoon, i recently failed my fault finding and have the same question... Do you take the cover off? Whats the process? Do i isolate the Main switch or leave that on and just isolate the circuit that i need to find the fault on?

Any help would be greatly apreciate
[/QUOTE]
For section C dont take the board cover off for the light circuit and DOL. Just the final 3phase whole board tests needs the cover off. For the lights test at the fitting and behind light switchplates too
 
Good afternoon, i recently failed my fault finding and have the same question... Do you take the cover off? Whats the process? Do i isolate the Main switch or leave that on and just isolate the circuit that i need to find the fault on?

Any help would be greatly apreciate
For section C dont take the board cover off for the light circuit and DOL. Just the final 3phase whole board tests needs the cover off. For the lights test at the fitting and behind light switchplates too
[/QUOTE]
Ok, take no board cover off. Unless you're isolating the whole board.

Once you isolate the lighting circuit go up to the light and test only at the light L-N L-E E-N Remember to activate the switches too.

DOL Motor test at the DOL
 
This post is getting a bit messy as its merged but basically the process is...
Ask permission for each of the 3 isolations. Lock off the circuit required. For the lights prove your voltmeter take the light fitting cover off a3md test L-N and E for voltage then reprove. For the DOL same but take the cover off (just) the DOL and test the incoming supply is dead. Prove -test-prove. Test the load side within the DOL noting that you wont have an N to test just in case a supply is coming from somewhere else and then your DOL is safe to work on. For the whole board same start but this time take the board cover off and Porive-test-prove the board itself. That should cover everything then
 

Reply to Safe isolation AM2 in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock