Currently reading:
SELV and 230V circuit separation

Discuss SELV and 230V circuit separation in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

K

knxhome

It is planned to install a central 24V SELV supply in a domestic residence, e.g. to power LEDs.

According to my reading, BS 7671:2008 chapter 414.4.1 (ii) requirements for protective separation between a SELV and 230V circuits offer the following options

a) double insulation -or-
b) reinforced insulation -or-
c) basic insulation and protective screening

for the highest voltage present.

Which value should be assumed here for "highest voltage present"? 230V or 230V plus potential voltage spikes?

Or to put it more simple: which cables (in the 1.5 to 10mm2 range) would be suitable for the SELV circuit according to option a), i.e. where SELV and 230V cables may run next to each other without further spatial separation?

Thanks in advance.
 
The highest voltage present means 230V.
If you intend running both the LV and SELV cables in the same trunking or conduit, then the SELV cable has to be rated for 230V.
 
The highest voltage present means 230V.
If you intend running both the LV and SELV cables in the same trunking or conduit, then the SELV cable has to be rated for 230V.

I have been inclined reading 414.4.1 (ii) the same way as you.
However, this appears to be a relative low requirement for the insulation.

According to the above interpretation the wiring of SELV circuit could be T&E, at least from the insulation requirement.
I certainly would not use T&E for a SELV circuit due to
a) potential confusion with the 230V circuits -AND-
b) earth should not be connected on the device side

Therefore, any suggestion for suitable SELV cables (1.5 - 10mm2) are still welcomed.
 
I have been inclined reading 414.4.1 (ii) the same way as you.
However, this appears to be a relative low requirement for the insulation.

According to the above interpretation the wiring of SELV circuit could be T&E, at least from the insulation requirement.
I certainly would not use T&E for a SELV circuit due to
a) potential confusion with the 230V circuits -AND-
b) earth should not be connected on the device side

Therefore, any suggestion for suitable SELV cables (1.5 - 10mm2) are still welcomed.
There shouldn't be confusion as selv runs should be kept to a minimum because of the current rating/ voltage drop; the transformer would normally be in close proximity to the load. To negate the worry you could label the T&E, "SELV".
Snip the cpc back to the outer sheath, it doesn't have to be used
 
There shouldn't be confusion as selv runs should be kept to a minimum because of the current rating/ voltage drop; the transformer would normally be in close proximity to the load. To negate the worry you could label the T&E, "SELV".
Snip the cpc back to the outer sheath, it doesn't have to be used

Planned is a CENTRAL 24V supply, as stated in the first post. Therefore the SELV circuits and LV circuits may run in parallel in certain sections of the house.

The problem of voltage drop has been taken into account.
 
Last edited by a moderator:
Please accept my sincerest apologies, I missed the "central" part. The selv should be earth sheathed if running in parallel to disperse any induced voltage. Hope this helps
 
Please accept my sincerest apologies, I missed the "central" part. The selv should be earth sheathed if running in parallel to disperse any induced voltage. Hope this helps

No problem, central SELV supply is not so common..... yet for LED illumination potentially attractive, due to their relative low wattage. Further it will be 24V and not the more widespread 12V.


Re earth sheathed:
The 24V supply will not carry any data signals. It is 24V DC, supplied from industrial-strength SELV-certified power supplies.
Therefore I do not see a need for earth shielding concerning EMI.
 
Last edited by a moderator:
Re earth sheathed:
The 24V supply will not carry any data signals. It is 24V DC, supplied from industrial-strength SELV-certified power supplies.
Therefore I do not see a need for earth shielding concerning EMI.[/QUOTE]
What will stop the higher voltage being induced into the elv cable
 

Reply to SELV and 230V circuit separation in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock