shower priority unit positioning

Discuss shower priority unit positioning in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
3
hi everyone, I'm in the process of converting an outbuilding into a granny annex which will have an electric shower installed I've been told I'll need a shower priority unit positioned in the main house next to the cu which will then feed the annex shower directly without need to involve the cu in the annex, what armoured cable will I need to supply both the annex cu for all the other circuits and shower independently , thanks
 
I have not got time to look in depth into it.
however my thoughts, right or possibly wrong as you have pointed out.

An isolator is a means of removing power from a circuit to allow amongst other things, work to be safely carried out on it.
a contactor by its very nature may bring power back to the circuit if it receives power to the coil, this may be from an automatic device like a thermostat or a remote switch.
I for one, would only rely on a contactor for isolation of a circuit i was working on under some very specific circumstances. and also, I have yet to see a contactor that has a means of locking off.
 

Reply to shower priority unit positioning in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock