Installed a garage CU, 2 way. As the house is TNC-S an earth rod has been installed, which is giving an Ra of 102 ohms.

The supply to the garage is protected by a MCB on the non RCD side of the CU, as installation methods don't require RCD protection.

The circuit in the garage has been protected by a 30ma type B RCBO. It is only single pole. I have today been told that it has to be of the double pole kind. Have I messed up?:confused:
 
As you have derived a TT form a TN-C-S then there is a possibilty of a PD arising between the combined neutral & earth of the PME and the true earth of the TT system under earth fault conditions should the RCBO operate and disconnect only the live.

Unless you are there to switch the main DP isolator off at ther same time, thiscan't be relied upon.
 

Reply to Single or double pole RCBOs??? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock