I am currently on a big flat development project (old high school being converted to 50 flats, plus a 3 phase landlord supply). I had planned on installing 25mm 3core SWA for all flat submains as the Flats are all Electric with no Gas.
However, i am now considering installing 25mm or 35mm split concentric cable as the installation method would not require RCD protection.
It seems to me to be an easier option when it comes to termination at both: the supply Main Fuse (installed via trunking at the Bemco Cupboard) & at the Flat Consumer Unit.
The area that has been designated for the Bemco Cupboard (for all 50 x Flats etc) is extremely small, hence the potential option of installing split concentric cable versus SWA.
I have come across this method of submain installation on many occasions but have i never personally installed it.

I would appreciate any advice regarding using split concentric cable & also the current capacity of such cable (some flats will be approximately 120m cable lengths).

Thanks - KevBen
 
Most of the concentric installations that i've seen, the terminations have all been a total mess!!
If you're going to go down that route always use heat shrink breakouts and sleeving on the cables head and tails. You can use amalgamated tape on the head, but unless you have plenty of room, that too can look a pigs ear of a job too!!


At least with SWA cables, they will be protected against accidental damage along the runs of cable from the intake room to the individual apartments...
 
Why would you need RCD protection if you used armoured cables ?

I had planned on installing 25mm 3core SWA for all flat submains as the Flats are all Electric with no Gas.
However, i am now considering installing 25mm or 35mm split concentric cable as the installation method would not require RCD protection.
 
Last edited:
So long as you don’t need RCD protection go for the split concentric.

Terminated correctly they look the dogs danglies. (Sorry E54, you don’t like the stuff, I do). It’s so much easier to handle than SWA. The sheath is as tough as old boots.

Please take care with the terminations, it’s all too easy to damage the neutral insulation.
 
So long as you don’t need RCD protection go for the split concentric.

Terminated correctly they look the dogs danglies. (Sorry E54, you don’t like the stuff, I do). It’s so much easier to handle than SWA. The sheath is as tough as old boots.

Please take care with the terminations, it’s all too easy to damage the neutral insulation.

what csa is the neutral & earth? In comparison to the Live?
 
The only concentric I’ve had dealing with were 35mm² solid aluminum line and equivalent hard drawn copper neutral.
Have a look on Doncaster cables web site for the CPC size.

The only time I’ve used split concentric was an office block. We normally worked to M&Q but we had exemption for this job. Due to the high loading from SMPS’s a separate CPC was run from the earth nest via the MET to each board. The incoming feed cables to the main switchboard were 4 core rather than the 3½ core we would normally have used. It was a bit of an odd bod job for me.

Working with concentric is great, you just have to be tidy in the way you break out the cable. The heat shrink boots and tubing make a great job of it.
The ones I did I used resin impregnated tape for the cable crutch. (It was a very long time ago :cyclist:) I don’t think you could get the HS break out boots then, if you could the company was as tight as a ducks bum and wouldn’t shell out for them.
 
So long as you don’t need RCD protection go for the split concentric.

Terminated correctly they look the dogs danglies. (Sorry E54, you don’t like the stuff, I do). It’s so much easier to handle than SWA. The sheath is as tough as old boots.

Please take care with the terminations, it’s all too easy to damage the neutral insulation.

I wouldn't go as far as saying i don't like Concentric cables, it's just that making the terminations can be a real ball's ache in tight spaces, and never look as neat as a well made off SWA.
 
OK, I'll back track a little, & appoloigise, you cannot use Split Con as SWA, you have to treat it as FLEX.
Look at the make up of the cable and the requirements for an SWA.

I still don't believe it is acceptable under BS7671, but, it will take time to cross reference & I have a PLC to finish programming tonight, or at least try, before I am due to go out for dinner with the family.
Keep the thread alive & I will post the reasons later, though IIRC I have before.
 
I have never used this (and I am never likely to) and I read this thread purely out of interest, but I seem to recall someone posting a while back (may have been Engineer 54) that split concentric should only be used in transmission work by DNO's. Have I mis-read that?
 
I have never used this (and I am never likely to) and I read this thread purely out of interest, but I seem to recall someone posting a while back (may have been Engineer 54) that split concentric should only be used in transmission work by DNO's. Have I mis-read that?

DNO’s use concentric cable N+E combined, PME. For large supplies they use 3 core wavecon concentric. That is a sod to work with.

Split concentric the N&E are separate by virtue of the neutral conductors each having an insulating layer.

Installed and terminated correctly split concentric is fine. If it wasn’t it wouldn’t get BASEC approval.
 
Ok, for a start:

543.4.7 No means of isolation or switching shall be inserted in the outer conductor of a concentric cable.

So you can't isolate the N, & there are requirements where ALL live conductors must be isolated.

There are others, I'm a bit busy @ the moment so not much time to reply, sorry
 
hmm , getting warmer with this debate now ;-)

following on from tonys post ,

pvc concentric cable was indeed developed for use by the dno's as it is lighter and cheaper than swa , flexible in the cold , and can be worked on live fairly easily as you know the live core is in the centre of the cable , making stripping it back alot safer with the power on.

which all means its great for the dnos.

the issues i have with its general use in buildings wiring is that the neutral conductors are not afforded the same level of insulation and protection as the live.
and as the earth conductors are bare anyway , it wouldnt take much in the way of abuse before you start getting crappy ins. res. readings between N & E.

all things considered though , its good stuff but its applications must be selected carefully.
 
Biff, nail on head!

Split concentric is for post DNO termination, concentric pre termination.

Handled and terminated right, its excellent cable. I’d much rather work with a 25mm S/C than the equivalent SWA.

I took a piece of DNO concentric and put a 1KV test on it. It took seven good clouts with a 2Lb hammer for it to even start breaking down. Not very scientific I know, normal test methods for me.
 
Biff, nail on head!

Split concentric is for post DNO termination, concentric pre termination.

Handled and terminated right, its excellent cable. I’d much rather work with a 25mm S/C than the equivalent SWA.

I took a piece of DNO concentric and put a 1KV test on it. It took seven good clouts with a 2Lb hammer for it to even start breaking down. Not very scientific I know, normal test methods for me.

That'll do for me.
I first saw the durability of MI shown to me in this way. A live piece of 2L1.5 with a lamp attached and lit was pounded with a lump hammer on an anvil. Was flattened to about an inch wide before the cable failed.
 
we use split con in my job on street lighting. we get a lot of neutral-earth faults with it. mostly dead shorts. Tend to use SWA as much as possible now on new installs & rewires as we find it a lot more reliable.
 
Never having terminated split-con or that I can recall, ever having seen it demonstrated, what is the correct/preferred method?
 
the issues i have with its general use in buildings wiring is that the neutral conductors are not afforded the same level of insulation and protection as the live.

Apart from the obvious one of the live being itself 'protected' by N & E, I can't see how that really stacks up? You've a 7 stranded core covered in one layer of insulation, and a N of 7 x singles (or small stranded) all individually wrapped to produce the same csa - so on aggregate that's far more PVC covering the N than the L!
 

Reply to Split concentric submains in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock