Currently reading:
Strange Call Out This Evening

Discuss Strange Call Out This Evening in the UK Electrical Forum area at ElectriciansForums.net

RED~SIX

Arms
Supporter
Reaction score
14
Had a quick call out to attend this evening. Currently closed but call was from a mum in need So I popped past with only my call out (light tools) in the car boot.

4 lights, one bathroom fan and a smoke alarm fed by a B6 MCB Protected also by an RCD.

Fault = no lights on the circuit working.
I quickly found the start and end of the circuit, so at the start I disconnected the loop so I could test the feed And work from light to light.
Using my fluke T5 the feed has the following:

Phase to earth = 240v
Phase to neutral = 35v
Neutral to earth 120v

the ceiling above is all a flat roof so no loft access.
I’m going back tomorrow for a proper look as I ran out of time.
Anyone had this type of fault before?
 
Had a quick call out to attend this evening. Currently closed but call was from a mum in need So I popped past with only my call out (light tools) in the car boot.

4 lights, one bathroom fan and a smoke alarm fed by a B6 MCB Protected also by an RCD.

Fault = no lights on the circuit working.
I quickly found the start and end of the circuit, so at the start I disconnected the loop so I could test the feed And work from light to light.
Using my fluke T5 the feed has the following:

Phase to earth = 240v
Phase to neutral = 35v
Neutral to earth 120v

the ceiling above is all a flat roof so no loft access.
I’m going back tomorrow for a proper look as I ran out of time.
Anyone had this type of fault before?
Any IR testing done?
 
The OP I believe has established that it is the supply cable from the the CU to the first light point which is faulty.

Hopefully it will be a broken wire in the CU or a joint in between, not so good.
 

Reply to Strange Call Out This Evening in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock