Discuss Tinned Copper cables ccc in the UK Electrical Forum area at ElectriciansForums.net

Spud28

-
Reaction score
11
Evening, has anyone got the current carrying capacity for old Tinned copper cables. Im looking at using an existing cable that looks just under 6mm (Imperial size most likely) for a cooker circuit. IR etc tests out ok. Thanks in advance.....
 
It is probably 7/.044 if it looks 6.0mm which is approximately 6.45mm so theoretically you can use 6.0mm ratings.
 
Evening, has anyone got the current carrying capacity for old Tinned copper cables. Im looking at using an existing cable that looks just under 6mm (Imperial size most likely) for a cooker circuit. IR etc tests out ok. Thanks in advance.....
 

Attachments

  • Imperial cable ratings.pdf
    57.1 KB · Views: 23
  • Imperial cable ratings.pdf
    57.1 KB · Views: 9
  • Imperial cable ratings.pdf
    57.1 KB · Views: 15
It is probably 7/.044 if it looks 6.0mm which is approximately 6.45mm so theoretically you can use 6.0mm ratings.
Thanks for the reply! Is there a chart or table as I would like to confirm on site. Cable definitely looks smaller than 6mm but bigger than 4mm. Cant seem to find any info....!
 
Thanks for the reply! Is there a chart or table as I would like to confirm on site. Cable definitely looks smaller than 6mm but bigger than 4mm. Cant seem to find any info....!
7/036 will be it then, I sent you a chart of sorts, I used that size for 30Amp circuits when I were a Lad, 7/029 was for ring mains as they were known in the past, the very distant past, Telectrix will know all about those cables as well as me and some of the oldies.
 

Reply to Tinned Copper cables ccc in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've tried to research and form a plan without asking on here, but I'm just going around in circles. Just completed an EICR. The wiring ranges...
Replies
15
Views
2K
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
326
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
1K
Hi, I have a book on domestic wiring which says that everywhere there is a change in current carrying capacity along a circuit there must be some...
Replies
3
Views
336
Good Evening. I’m currently carrying out an EICR. I have a cooker circuit radial with a 32amp mcb fed from and RCD split board. There is a 45amp...
Replies
14
Views
955

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock