Is that at 230V?Did a little online research into caravan aircon units, and it turns out they draw less than I expected. A popular Truma model only draws 4.2A (albeit with a hefty 28A start up surge for 150mS).
From the above, it might make sense to look at 10A C-curve RCBOs so they won't trip on the start-up of the A/C but the folks know they can't push too far.Supplies definitely won't be metered, if you want customers to return.
That seems quite reasonable. I would be inclined to still use a delay-RCD for fault to earth protection and then look at pushing the OCPD up as far as sane to get better selectivity with the RCBOs and so a short-term overload causes a brown-out instead of a total cut off.In the apparent absence of any national standard for diversity, I was thinking along similar lines to R-fur above.
6A per caravan/motorhome outlet and 2A per tent outlet, gives a total design load of 50A, spread over the two available phases, so 25A each.
Cables sized to give 5% drop at the furthest socket, assuming the full 16A drawn from that socket, and 6A - 2A being drawn from the other points along the route.
Sound about right?
For example, if you are looking at 6mm you could even look at a 40A D-curve MCB (Hager selective to about 0.5kA with thier 10A C-curve RCBOs), as a 300mA delay RCD would meet your disconnection time on cable faults, while being selective to a 100A supply fuse to 4.2kA
If the supply fuse is smaller, say 60A, then you would be limited to something like a 32A D-curve or 40A C-curve to have any supply-side selectivity, and then load-side selectivity is down in the 0.35kA region.
Or use a 40A switched-fuse which would be better for selectivity both ways, but I doubt that is so good here due to the hassle of the owner having to replace a fuse if a fault to really bad diversity situation occurred.