Transformer causing mcbs to trip

Discuss Transformer causing mcbs to trip in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
5
Hi. Could someone confirm weather you think I'm right or not. Today I installed a ceiling mounted suspension wire lighting track in a domestic kitchen. It's fed via a fairly chunky wire wound transformer (I don't know the kva of hand). The mcb supplying the circuit is a type b 6 amp rcbo. Pretty much most of the time I flick the switch to turn it on and also when I turn it off it trips the mcb.

im thinking I need to change the mcb to a type c to manage what appears to be an inductive load caused by the wire wound tranny. Would you guys agree or suspect something else?

thanks in advance..
 
you are on the right lines. for e.g. a 3kva 240V/110V site transformer will only pull 13A@ full load, but even unloaded, will trip a 16A MCB on start-up. a type C MCB is advised.
 
Fitted some suspension lamps in a kitchen a few years back. Tranny was massive and hummed like bu$gery. Changed it for an electronic transformer. Worked a treat, plus it can be dimmed. You won't get any inrush current issues with one either
 
Once a week I used to switch a 2000KVA transformer on. It even frightened me when it shot of scale 200A+ @11KV.

Have a look on Google for "transformer inrush and magnetizing currents" if you want to understand why it happens, otherwise just stick a C or D MCB in.
 

Reply to Transformer causing mcbs to trip in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock