Search the forum,

Discuss TT eicr code? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

If you have a fault where the resistance is between 7660Ω and 2300Ω then the RCD would (probably) not trip in <0.2 s however it is not required to according to BS7671. This would be a similar situation to MCBs that will not trip in the required time if the fault current is low; similarly how do you know and MCB will trip in the time stated, you do not know, you are relying on the manufacturers making them to standard. It is not (in standard situations) safe to test this compliance.

You are quite right, however we still record the disconnection time on a 100mA at 1x and 1x only. This is the disconnection time at its rated current, which is higher than 200ms, therefore it will not comply.
 
You are quite right, however we still record the disconnection time on a 100mA at 1x and 1x only. This is the disconnection time at its rated current, which is higher than 200ms, therefore it will not comply.
There is a difference between the requirements to meet disconnection times and the requirements to test if the RCD functions.
The disconnection times would be met so long as the Zs reading complied.
The 100mA time delayed RCD tripping in >130ms<500ms at Idn shows that it is working.
 
OK I think I am at a loss to explain here.
The disconnection time of 0.2s for a fault of negligible impedance, which is required by the regulations, would be met.
The RCD would not necessarily disconnect in 0.2s under all circumstances but this is not required at all by the regulations.
 
If anyone is going to base whether an installation is safe according to the regs at the time of the installation, they would need to know the date of installation, how often are we blessed with this information? Once upon a time fused neutrals were considered a good idea. Its really up to the individual at the time to make an educated assessment of coding required, many amendments are for the better, some have taken a backward step IMHO. I like to base my decisions on worse case scenarios, can't go far wrong then.

If you were experienced, you would/should be able date an installation to a regulations edition, with some accuracy. Unlike today, Regulations didn't change at anywhere near the regularity they do today... Unfortunately we have 17 day whizz kids and electrical trainee's undertaking/conducting EICR's that haven't got a clue what they are looking at, let alone being remotely able to make an educated assessment. Depends on what you mean by ''worst case'', ..if that means assessing a totally improbable scenario, as being possible, what is that saying?? lol!!
 
So what was actually wrong with the long standing previous 0.4 second disconnection times?? Which i might add, is still the disconnection time value for many countries around the world, as well as TN ADS systems in the UK!!
 
No matter how experienced one is, you could never always prove that an installation was installed as per requirements at the time.
I've been in this game 42 years this coming June , and I'm still blimim learning!
I like to try and keep up to date, and have many reference books at my side, its great to know they will all be out of date again come next January. You are certainly right about regs not changing like they do today.
 
So what was actually wrong with the long standing previous 0.4 second disconnection times?? Which i might add, is still the disconnection time value for many countries around the world, as well as TN ADS systems in the UK!!

I never said anything was wrong with them, just that where an RCD is used for fault protection on a TT system the maximim permitted disconnection time is now 0.2s. Higher than this is considered unsafe by BS7671:2008
 
No matter how experienced one is, you could never always prove that an installation was installed as per requirements at the time.
I've been in this game 42 years this coming June , and I'm still blimim learning!
I like to try and keep up to date, and have many reference books at my side, its great to know they will all be out of date again come next January. You are certainly right about regs not changing like they do today.

Then you should have no problem dating an installation to a reg's edition. lol!! I didn't say you shouldn't test, ....testing is the only way you are going to be sure of any findings you make. Now come on, after 42 years in the game, do you really NEED all those installation by numbers OSG's etc??
 
I never said anything was wrong with them, just that where an RCD is used for fault protection on a TT system the maximim permitted disconnection time is now 0.2s. Higher than this is considered unsafe by BS7671:2008


Do you get ''deaded'' faster with a TT installation than a TN one then?? Or is it more about ensuring that RCD protection is included into all TT installations to prop up their 200 ohm Ra value?? lol!!:wings: Don't take this post too seriously now will you!! lol!!
 

Reply to TT eicr code? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

See this time after time - poor installation: new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The...
Replies
2
Views
414
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
So I'm getting various responses to this depending on how things are interpreted. Here's a scenario: Assume property is a tenanted property...
Replies
25
Views
2K
I am a landlord and my managing estate agent just recently organised an electrician to carry out EICR. Came back as unsatisfactory, no RCD...
Replies
27
Views
8K
Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top