Can someone let me know the wiring procedure when underflooring heating is being installed by flow and return piping,and seperate room stats are required for rooms.so six rooms and each room having its own stat which are wired and not wireless.
 
If it's a y-plan and there not piped individually with actuators for the stats to open them, the only way is all stats in parallel and if any one of them calls it will bring the whole heating side of system on, bit rubbish if this is the case.
 
You need to know what equipment he is installing in terms of manufacturer.

Underfloor heating for 6 zones will need a central controller that communicates with the room stats/controllers and controls the manifold valves. Depending on the manufacturer you could need:
simple T & E
4/5 core cable
or even ethernet type cable.
 
Depending on which type of Programmable stats your using, but for example if it was a heatmiser 12v system I would have a cat5 from each stat back to my wiring centre, then were ever your zone valves are, have at least 3 cores back to your wiring centre there. The wiring centre (UH1) would be near the manifold I hope, therefore your pump, pipe stat and zone actuators can all be surface...
 

Reply to Underfloor Heating in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock