What are these transformer looking things I have been seeing?

Discuss What are these transformer looking things I have been seeing? in the Australia area at ElectriciansForums.net

Reaction score
4
Hi.
I have seen these transformer like things on the higher voltage powerlines when I go to regional areas in NSW and I was wondering what they are? I can't remember seeing them where I come from (Central Coast NSW)
They couldn't be transformers because they are not connected to any other wires.
Would love any insights.
IMG_2835 2.jpeg

I am just a science teacher who loves to learn what he sees
 
Surprisingly one of my old colleagues is on shift tonight in Western Australia (Western Power), I sent him a message and he thinks it may be an SF6 load break switch by insulect (it's an Australian make).

Cannot believe he answered so quickly, he must be bored in the control room!

 
Surprisingly one of my old colleagues is on shift tonight in Western Australia (Western Power), I sent him a message and he thinks it may be an SF6 load break switch by insulect (it's an Australian make).

Cannot believe he answered so quickly, he must be bored in the control room!

Oh wow! Thanks for that. I had a quick look, but it is really late here… I’ll read and process it in the morning.. ha ha..
Thanks so much for that!
 
Surprisingly one of my old colleagues is on shift tonight in Western Australia (Western Power), I sent him a message and he thinks it may be an SF6 load break switch by insulect (it's an Australian make).

Cannot believe he answered so quickly, he must be bored in the control room!

Thanks for that Julie. I am just back from holidays, and have a bit of a chance to reflect on all the things i saw.
So basically they are used to open the circuit to perform maintenance, etc?
Is the SF6 used so that the electricity doesn't arc between connections? I actually already knew that SF6 is an important electrical insulator.
 
Thanks for that Julie. I am just back from holidays, and have a bit of a chance to reflect on all the things i saw.
So basically they are used to open the circuit to perform maintenance, etc?
Is the SF6 used so that the electricity doesn't arc between connections? I actually already knew that SF6 is an important electrical insulator.
SF6 is used to reduce the size of the equipment. That looks like a 33kv line, maybe an 11kv. An air-break switch at that voltage would need much larger separations so would either be out in the open and subject to weather/birds etc. or much bulkier if enclosed.
 
Thanks for that Julie. I am just back from holidays, and have a bit of a chance to reflect on all the things i saw.
So basically they are used to open the circuit to perform maintenance, etc?
Is the SF6 used so that the electricity doesn't arc between connections? I actually already knew that SF6 is an important electrical insulator.
Yes, they are basically a switch just for routine switching, so open for maintenance, general stuff etc, if there happens to be a fault on the line it can close safely, but cannot open or disconnect in the case of a fault. - it's the closest thing to a light switch! You open and close as you need to but in the event of a fault it isn't the light switch that opens, it's the breaker upstream (in your main panel at home)

SF6 is used as it's both a better insulator than air, but also quenches the arc better than air.

Traditionally high and medium voltage switchgear tended to be oil filled - however although there are some advantages, the resulting explosion in the event something goes wrong internally is a huge bleve - this fireball can be very destructive so the trend is away from oil to SF6, or vacuum equipment.
 
Yes, they are basically a switch just for routine switching, so open for maintenance, general stuff etc, if there happens to be a fault on the line it can close safely, but cannot open or disconnect in the case of a fault. - it's the closest thing to a light switch! You open and close as you need to but in the event of a fault it isn't the light switch that opens, it's the breaker upstream (in your main panel at home)

SF6 is used as it's both a better insulator than air, but also quenches the arc better than air.

Traditionally high and medium voltage switchgear tended to be oil filled - however although there are some advantages, the resulting explosion in the event something goes wrong internally is a huge bleve - this fireball can be very destructive so the trend is away from oil to SF6, or vacuum equipment.
Interesting about the oil. Thanks for your reply.
Thank you so much for discussing this with me.
 

Reply to What are these transformer looking things I have been seeing? in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top