Search the forum,

Discuss What would you code this as. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

If the SWA gets damaged, ie L-E or L-N fault, I should imagine the current will be a lot more than 80A, possibly nearer 800A (irrespective of whatever mcb’s/circuits are connected downstream), resulting in a fried cable and an expensive replacement for the sake of proper over current protection.
 
Im not saying these faults don't happen i'm asking about OP claiming the client was 'lucky' because the cable 'could pull 80a' because there's an 80a main fuse. I'm just talking about the installation as it is now not under a situation where it may develop a fault.

Isn't it only the equipment the other end that can pull 80a, which would never happen since it's lighting and sockets protected by 6 and 16 amp MCB's?
There is always the possibility of one of the downstream devices failing to trip - contacts weld together or the mechanism itself fails, upstream protection will limit the extent of an overload in these circumstances; nevertheless I would tend to agree, overload protection is probably not necessary on the swa, however fault protection still is, and as it's the same device its omission raises a c2.

The semantics aside the customer was lucky - especially given the numerous glaring issues that exist in merely this one photo.
 
Is it just me or has this thread just revealed a tragic lack of understanding between fault protection and overload protection? This is basic stuff ladies and gents.
 

Reply to What would you code this as. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

So a quick catch up so you can get an idea… I was asked to do a job for another electrician, as he is too busy. I’m busy myself but said I’d...
Replies
18
Views
2K
Hi. This is a gloriously messy installation I looked at this morning at a house a friend just purchased. It t became quickly clear it was more...
Replies
7
Views
1K
Yes, it's another EICR coding question - hurrah! :blush: Inspecting a small 1 bed 70s ex-council flat that was going well. Main Bonding had...
Replies
12
Views
7K
I’d like your opinions on a scenario I’ve come across. A certificate was produced which contained errors and while there were still faults on the...
Replies
9
Views
2K
Customer calls and asks for a quote to repair her garden lights. all fed from a board in the outbuilding/summer house. She is in her late 60s her...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top