Been to look at a fuseboard upgrade.


The house has a 3-phase cutout. One phase isn’t used, and the other two phases feed a single phase meter each. The house therefore has two single phase meters, each feeding an old wooden Wylex board.


One meter/board does lights, garage and a few sockets, the other does mostly sockets. Can’t see any obvious reason why it's set up like it is.


Can anyone see any issues with me getting one of the supply phases de-energised and installing a new consumer unit for the whole house, on one phase?


It’s big 6-7 bedroom house but the overall energy usage would be fine on one phase. They’ve got 2 8.5kW showers, a double oven and usual lights and sockets.


My only concern is that the DNO likes to balance loads between phases. Am I doing anything wrong by putting all the customer’s demand onto one phase?


I don’t know what size fuses are in the cut-out as it’s still sealed. And no, it's not economy 7 or anything like that.



Thanks in advance.
 
Simple explanation for this would be that they had a second phase connected at some point in time and didn't have a meter capable of working on the two phases with them on the day the board came to connect.

Just get the meter operator out to swap it for a single meter on the two phases, they won't then have to pay the two standing charges
 

Reply to why has house got two meters? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock