Currently reading:
Zs reading high on external lighting

Discuss Zs reading high on external lighting in the UK Electrical Forum area at ElectriciansForums.net

cliffed

-
Arms
Supporter
Reaction score
650
Fitted 2 new external lights onto existing cabling, their on a remote wall quite a distance from house.
My mistake was not doing a Zs before I started the works.
Finished & tested Zs reading 14 ohms.
Its a Tncs supply quite a big install…the lights are supplied by a 6 amp C type MCB.
Reported this to the Client & my Boss…still no feedback on what to do.
I”ve suggested a Rcbo to protect this circuit & FI TO take place.
Windering your thoughts on this.
 
Have you done a Ze and dead testing of the circuit as you need to confirm if 14 ohm is actually a realistic reading for the circuit before you fit an rcbo which may be an inappropriate course of action.
 
Fitted 2 new external lights onto existing cabling, their on a remote wall quite a distance from house.
My mistake was not doing a Zs before I started the works.
Finished & tested Zs reading 14 ohms.
Its a Tncs supply quite a big install…the lights are supplied by a 6 amp C type MCB.
Reported this to the Client & my Boss…still no feedback on what to do.
I”ve suggested a Rcbo to protect this circuit & FI TO take place.
Windering your thoughts on this.
What other tests have you carried out? why a C type mcb?
 
Have you done a Ze and dead testing of the circuit as you need to confirm if 14 ohm is actually a realistic reading for the circuit before you fit an rcbo which may be an inappropriate course of action.
Agree but @ this moment there is no earth protection on that circuit.
Or never ever been any earth protectio….regarding the high loop impedance.
 
1 - Are you happy with the earthing in general? You need to be sure that the supply is fine before you consider the circuit. Hence request to do Ze or at a minimum if you can't isolate Zs@DB.

2- Is it realistic that you have (quick smoke packet maths) around 300m of 1mm or almost 500m of 1.5mm on this circuit?
 
Regarding the high loop impedance
 

Attachments

  • E068C0EB-78E8-4760-AC17-C7784C6AB901.jpeg
    86.2 KB · Views: 35
1 - Are you happy with the earthing in general? You need to be sure that the supply is fine before you consider the circuit. Hence request to do Ze or at a minimum if you can't isolate Zs@DB.

2- Is it realistic that you have (quick smoke packet maths) around 300m of 1mm or almost 500m of 1.5mm on this circuit?
Not sure about the length of circuit. this was a like for like replacement I’ve done all I can reported to all…asked for existing Certification & basically no feedback whatsoever.
Im not happy with the Zs & suggested an Rcbo to give protection & FI will be required.
 
This needs a sample of R1+R2 readings on the circuit at various points along it. Even 2 or three more would tell you a lot.
Unless it's truly a giant circuit and the readings progressively increase along it's length there is probably loose connection somewhere.
(If it really is a circuit that big I'd also be running some volt-drop calculations, it may not comply with max 3% volt drop on lighting circuits.)
 

Reply to Zs reading high on external lighting in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock