Zs reading with main earth disconnected

Discuss Zs reading with main earth disconnected in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
39
Morning, just checking a lighting circuit on a house, I have the main earth disconnected and still get a zs reading of 2.2 ohms. No evidence of an earth spike and bonding goes direct to henley block.

Any suggestions why this could happen??
 
So you've got a circuit with a CPC present in at least one fitting, but no CPC present at the DB, and you want to find out where that CPC is getting its earth from, to decide whether it's trustworthy?

If it were me, I'd turn the board off, maybe separate out the CPCs, null out a nice long wander lead, clip the end of it on the CPC and probe various likely contenders around the house with the meter on low ohms, to see which gives the lowest reading and hence is the likely tap off point. I can't see any advantage investigating this live, but many disadvantages.

Or, since it's at least a bit of a bodge, maybe a lot of a bodge, declare the circuit CPC-less and treat accordingly.
 
Depending on circumstances, main earth may need to be disconnected to verify certain fault conditions..
All comes down to knowledge, understanding what is going on and being in control of the location.

What conditions would they be?
I can't think of any reason to have an installation which relies on ADS energised without its connection to the earthing system.
 
I have also disconnected the main earth to demonstrate to apprentices how parallel earths can appear to drag down the Ze or Zs readings of a TT installation.
I have also disconnected the main neutral to demonstrate how this can be dangerous..
 
Whatever the justification for energising some hypothetical system with the earth disconnected for demonstration or analytical purposes, the OP had a specific task in hand which was to trace a connection to a section of CPC that did not seem to start at the origin. As such, it's a simple continuity test to the MET, other CPCs or mass of earth, that does not require the system to be energised to trace. There is no justification here to work with the system energised.
 

Reply to Zs reading with main earth disconnected in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock