Recent content by Adamk

  1. A

    Cooker supply 12kw correct cable size

    Hasn’t took diversity into account... he’s just done 8600/240 which isn’t correct.... but mainly causes he’s ran out of beer
  2. A

    Cooker supply 12kw correct cable size

    True, but you charge the customer the extra money for the bigger size cable and it’s no real difference running it in. Even though it comes out at 30a I’d say you were pushing the boundaries. Nothing wrong with what your saying, just rather chuck a 10mm in. If I would of known my customer was...
  3. A

    Cooker supply 12kw correct cable size

    well if 6mm goes up to a total of 14/15kw and his is 17.7kw next cable up is 10mm and that’s a 40a breaker and obviously double cooker switch is rated at 45amps, might aswell do 10mm from the load to cooker aswell. My personal choice.
  4. A

    Cooker supply 12kw correct cable size

    Must be 10mm on a 40a mcb... with the cooker switch rated at 45amps... my personal choice
  5. A

    Cooker supply 12kw correct cable size

    Yes this is the 1st time this has happened after many many kitchen jobs. Howdens muck up the kitchen layout and they had more space where the cooker was going to go, so they Thought they would go for a wider and more powerful as they had more space.... Not ideal
  6. A

    Cooker supply 12kw correct cable size

    Have to charge her extra for the heated screed
  7. A

    Cooker supply 12kw correct cable size

    Nope, not at all. Run back the board is near no pipes or rads
  8. A

    Cooker supply 12kw correct cable size

    Well the things is that it’s inside a 25mm conduit under some screed for about 5metres... rest of it’s under the floors boards so got Plenty of air. Thoughts?
  9. A

    Cooker supply 12kw correct cable size

    Hey guys I’ve run a 6mm for a cooker, runs about 10metres. The customers has changed her mind on the cooker and gone for a 12kw range. Went back today to finish off and saw this lovely surprise. I know you have to take diversity into account. But for my peace of mind. Would 6mm 32a MCB be fine...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock