    Advice Wanted - VERY High Earth Resistance Problem

    Stima, the main reasons for the extra earth rods were to fix the ends of the tape to them, mainly for testing, I just wanted to have each end of the triangle that I have made a testable point, just for my own peace of mind, the highest vale tested was what I recorded nearest the property anyway...
  2. Axnfell

    Advice Wanted - VERY High Earth Resistance Problem

    Managed to get it down to 112 Ohms, after paying out a small fortune, 3 earth rods later all connected with flat copper tape (25mm x 3mm x 25m) dug into the ground about 12” deep, couldn’t get any deeper due to roots and rock. Thanks guys for the advice
  3. Axnfell

    Advice Wanted - VERY High Earth Resistance Problem

    They kind of live in the middle of woodland, on a hill that seems to be basically baserock with a light covering off soil and roots, all looks lovely but a real pain at the moment, I have not tried Tape yet, I was kind of hoping that this would be a simple fix somewhere along the line, Will have...
  4. Axnfell

    Advice Wanted - VERY High Earth Resistance Problem

    Earth Rods are being hit in to their entire length, approx 1m deep, cannot get much deeper as we are hitting bedrook, have tested using |KEW-5105A and then tried removing the earth rood and testing again 1 meter further away from the property and so on, but cannot get the reading to get any...
  5. Axnfell

    Advice Wanted - VERY High Earth Resistance Problem

    Hi, Yes trying to test 'Ra', Here on the Isle of Man most of the Island is TT based Earthing.
  6. Axnfell

    Advice Wanted - VERY High Earth Resistance Problem

    I have been doing some tests around our property here and I cannot get the earth resistance test to get anywhere lower than 1.86k, even started tested now up to 30 meters away from the property and still cannot get any lower readings. Any advice would be greatful. Kind Regards James

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock