    Air conditioning installation - supply options

    No problem, I will do that. Turns out I have a spare 20a MCB on the RCD protected side running a radial circuit to a single unused socket. I will re-purpose this to become 2x FCU.
  2. B

    Air conditioning installation - supply options

    Combined maximum load (when on heat mode) is 2x 7.5amp = 15amp. Thought if I could use just 1 of the remaining 2 MCBs it still leaves me with a spare. I did toy with the idea of using RCBO's, but finding stock of a 16amp MK RCBO is proving difficult. I'd also still need 2x FCU with the RCBO...
  3. B

    Air conditioning installation - supply options

    Thanks Pete. I think I will use those RCD FCUs even if there is no requirement from the manufacturer. I'd rather have a belt and braces approach when it comes to safety. I believe I am right in saying I can use just one of the C16 MCBs to feed both RCD FCUs with 2.5mm twin and earth, one...
  4. B

    Air conditioning installation - supply options

    Thanks Pete, I think thats the route I will go down anyway - even if not specified by the manufacturer. I understand that only one of the MCBs needs to be used to feed both RCD FCUs, one spurred off the other.
  5. B

    Air conditioning installation - supply options

    Ok thanks, I will check the manufacturers documentation. If it does not state I think I would prefer there to be RCD protection due to the fact there is power to the outside units. All cables will be surface mounted in conduit.
  6. B

    Air conditioning installation - supply options

    Hello, We are having 2 wall mounted split system air conditioners installed. These come supplied with a 13amp plug which will power both the internal and external units. I would like to wire these in for a more permanent and neat installation. Our consumer board only has a single "RCD...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock