  1. J

    Rcd fails test.

    Hawk moon, I will try your suggestion tomorrow, I've got to prove rcd, either is duff or that there a fault elsewhere. Thanks to everyone for all the advice, as always it's helpful.
  2. J

    Rcd fails test.

    Ze is 0.13 and zs for shower is 0.38.
  3. J

    Rcd fails test.

    Hi, live in northern Scotland, hence distance to supplier, nothing is close by. It's a Wyler shower cu.
  4. J

    Rcd fails test.

    Time to remove rcd and return it to supplier and get a new one and the cost of a forty mile trip.
  5. J

    Rcd fails test.

    Onions, thanks for that, that was what I was thinking, i was beginning to think I had missed something. But as the r1 and r2 and insulation tests are ok there shouldn't be a damage to the cable. I checked all connections were tight in both the shower and the switch unit.
  6. J

    Rcd fails test.

    I'm familiar with my tester, I ran the test at both at the shower end of the circuit and the consumer unit end. I had to pack up due to child care issues otherwise I would have spent longer longer looking for the fault. To double check my tester I checked the properties other rcd using the...
  7. J

    Rcd fails test.

    Hi, I've been installing a new shower, using a shower consumer unit complete with rcd. All the tests passed, r1 And r2 were 0.23 ohms, insulation resistance was >299M ohms, polarity was correct. But when I test the rcd I cannot get it to trip. It passes when the test button is pressed but will...
  8. J

    Starting a new career in Scotland

    Hi, I'm new to all this, after 22 years service as an RAF aircraft engineer, I'm now looking to start out in the civilian world. My father in laws an Electrician, in England, time served and just about retired, he rewired our house a few years ago, with my assistance, on his advice I compleed...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock