Recent content by Martin Flint

  1. M

    Excessive earth fault loop impedance

    Many thanks o did s bit of digging and worked out 0-24 so I knew they all comply but thanks for your help
  2. M

    Excessive earth fault loop impedance

    Hi sorry for delay I’ve been to the job and they are protected by Berlin gerun BS100N Mccb I have 3 phase 100a and single phase 63a and 32a they are saying max zs is 0.10 for these can anyone confirm or tell me what the max zs is for these many thanks
  3. E0B12D01-F8F6-468E-8F50-A3E81EBF2580.jpeg

    E0B12D01-F8F6-468E-8F50-A3E81EBF2580.jpeg

  4. 51A99293-C3AA-4CD2-90DA-1B59E1DD7DDC.jpeg

    51A99293-C3AA-4CD2-90DA-1B59E1DD7DDC.jpeg

  5. 7076F013-1A75-46BF-9B32-FF3DB454EC56.jpeg

    7076F013-1A75-46BF-9B32-FF3DB454EC56.jpeg

  6. 6F225430-8407-404D-8D8B-4BC206C4AF23.jpeg

    6F225430-8407-404D-8D8B-4BC206C4AF23.jpeg

  7. 2F200605-9FA2-4B4B-9A42-BE5AC05E8A39.jpeg

    2F200605-9FA2-4B4B-9A42-BE5AC05E8A39.jpeg

  8. M

    Excessive earth fault loop impedance

    I’m going to the hotel tomorrow to have a look will provide more info then but if it is the ze wouldn’t all the circuits have a high reading ? Also regarding zdb is the ze from another dB recorded as a zs reading ? Many thanks for your reply
  9. 395BCEB0-7110-44BC-B0DD-69A0583B574E.png

    395BCEB0-7110-44BC-B0DD-69A0583B574E.png

  10. M

    Excessive earth fault loop impedance

    I work for a hotel chain and recently we’ve had our 5 yearly test they have 8 circuits from our LV panel with excessive loop impedance readings !! So apart from either introducing an rcd or dropping mcb ratings or type is there any other way of achieving satisfactory readings ?? Also if I have a...
  11. M

    Advice on5 year periodic test on hotels

    I’ll Hi I need a bit of advice on our 5 year test the company has put a limitation on checking main fuses and bussbar testing due to the gas meter adjacent in the room !! 5 years previous this was not picked up is this acceptable or should they do this ! Many thanks for your help Also they...
  12. M

    Max Zs for Bs88-2 630amp fuse

    Hi Andy if you could pass this on would be great
  13. M

    Max Zs for Bs88-2 630amp fuse

    Oh I see many thanks for your help
  14. M

    Max Zs for Bs88-2 630amp fuse

    And you think the reading is not realistic because of the transformer ? How would you recommend putting a resistance on the circuit bearing in mind it's an open occupied hotel ! Sorry I've never come across this problem and not really tested bussbar

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock