Thanks, appreciate all of your comments, although this unit is on wheels (at the rear) and towed I think I'll stick with my original coding as placements are usually for months at a time so any movement that may effect the installation is minimal.
While I'm at it, any opinions on SY being...
Yes, not frequently but it does have various locations. It's an NHS Mobile Breast Screening Unit. Don't know exact size but would say around 11m x 2m.
Referring to Regualtion 717.52.2
Hi all,
I've recently carried out an EICR on a transportable unit and all circuit wiring has been installed in Twin & Earth. According to regs only flexible cabling should be used due to frequent movement, vibrations etc. I myself wouldn't deem this as needing urgent action and think it would...
Hi all, back again requiring some transportable building knowledge, this time round a catering/burger van and its earthing arrangment.
Was asked to carry out some simple repairs and replacements to a local burger van that is basically static to one location. Fed by a 3kva generator with a16a...
Hi all,
Just carried out an EICR on a transpotable classroom. Trying to decipher a reg to see if something is compliant. 717.411.1 States automatic disconnection of supply shall be provided by RCD not exceeding 30mA, now does this refer to the site supply (which cannot be certain due to...
Thanks for your replies, it's been discussed with the client and agreed that dead tests and a visual wil be sufficient. Seems so BrightSpark, the link to purchase the TCN4 cert was broken so searched through the NIC store and they had this notice in the DPN7 cert description -
This report also...
Hi guys,
Firstly, hello :seeya:, new to the forum.
Have been asked recently to carry out an EICR for a couple of mobile classrooms so knowing that they're a special location, spent a while trawling the forums for previous threads on the subject but not much information to be had. Did suss...