Hi pawel, I was an industrial installation electrician who went into being a maintenance engineer about 3 years ago, I am not sure what your job description is but I was a multi skilled engineer for a cardboard manufacturer and printer in Yeovil, expect lots of pump rebuilds, pneumatic...
Hi all, happy new year and apologies for the late reply, we have cracked the issue, it was sort of related to lack of neutral at the transformer although the voltage drops were also a symptom really.
First of all, I connected a neutral to the supply side of the auto transformer (although...
Hi marconi, thanks for your reply, it's been a while since I've thought about it, but I don't think it would cause to many problems if I connected the supply Neutral to the auto transformer, as shown in part of the link you have posted, we would then have somewhere for the zero sequence current...
Hi all,
Been a few years since i've posted but here goes! At the factory I work in we have an old Spanish line from the mid-eighties that is fed from uk 400v 3 phase via a 3ph step down autotransformer to give 380v output.
The spanish panels Do not use a neutral, just 3 phases and further 380v...
Which is a valid point DillB, I suppose we could go down the lines of leaving a notice inside the board etc. But we are talking domestic in this situation, I have only personally done it to fit 6A RCBO'S to lighting circuits and I would do it again.
It's one of those modifications they...
And the very same manufacturer now supplies smaller busbar, and smaller terminals on their new MCB'S. Granted the makeup of the copper could be different etc. But if your connecting a 6A load to a slightly filed down busbar which was rated at 63A per way, I don't think using common sense you...
I have had it before with MCB's, I replaced tthem as I thought it's obviously a high resistance connection, probably on the contacts, losing half an ohm is quite a lot.
Yes perfect sleep thanks, we're hardly talking a lot of filing, if you measure the bar, there much bigger then the modern equivalent, and if you were really picky you could calculate the csa of the remaining busbar lug and see if it was adequate for the load.
Or replace the whole bar with a new...
Some call it a haircut lol
On a serious note, cable haircuts are bad, but if you have a look at the size of the old memshield busbar, it's huge compared to all other makes, you could just buy a generic 100A busbar and it would be a hell of a lot smaller then the filed down original.
I couldn't...
PLC'S are quite simple really as far as on site maintenance goes, usually I just confirm that it is a plc issue and we get a local chap in go reprogram, normally it's a faulty relay output and he just modifies the program to use a spare output then change the wiring over, to be honest, most...
Hi mate, I've recently just transferred myself and love it, if your a practical chap, you'll be fine, mist of my work is mechanical, pneumatic, hydraulic as well as electrical though, even have to unblock bogs occasionally as well as changing lamps fitting doors etc.
That's the battens I always use, their cheap at £26 each and seem to last the distance, why anyone bothers with cheapo makes I don't know. The only fault with the thorns is that don't bother to secure the cables inside.