Evening all...
I have just got back from a CU change. All was going very well and I was finishing early which was lovely for a friday evening, and then.......
The RCD on the opposite side to the lights trips when the lights are switched on... arghh. I eventually found the problem, I had screwed through the shower cable when attaching the CU to the piece of wood I was using to hang it on.
Whilst the screw was still through the shower cable (touching N-E) why did this stop the test button from working on the RCD? There was 240V going through the RCD and by using something on the other side of the dual RCD board it would trip, but it would not trip with the test button?
Cheers.