Discuss 16mm tails on 100A cut out in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

No, as far as I know there is no requirement for the DNO to make their equipment suit the customers installation. They provide a standard size and type of supply and it is up to the customer to ensure that their installation is suitable.
I was thinking about how they (from posts I've read) refuse to connect things they don't like - such as refusing to connect a supply to 16mm tails. I'd have thought their ESQCR would have something to say about connecting a supply when it's clear there is equipment in-line that is not rated for the current rating of their fuse.
I'd have expected them to offer 3 choices: stay with a 60A fuse, change the VOELCB to one rated for 100A and we'll fit a 100A fuse, or stay without a supply.
 
I expect they only refuse if they think it is a risk to thier side (say cable not suited to the cut-out or meter terminals) or the installation is unsafe.

Your Wylex board is only 60A rated, the sum of its fuses is probably less than 60A, the VOELCB (if working) is adequate for the installation as it was made at that time. It is not for them to decide if you should upgrade or not providing it is not unsafe as such.
 
I was thinking about how they (from posts I've read) refuse to connect things they don't like - such as refusing to connect a supply to 16mm tails. I'd have thought their ESQCR would have something to say about connecting a supply when it's clear there is equipment in-line that is not rated for the current rating of their fuse.
I'd have expected them to offer 3 choices: stay with a 60A fuse, change the VOELCB to one rated for 100A and we'll fit a 100A fuse, or stay without a supply.

I have no experience of a DNO refusing to reconnect an existing installation after carrying out any work to their equipment.

However in my experience some DNO operatives will find any excuse they possibly can to avoid starting a job or to refuse to connect a new installation.
 

Reply to 16mm tails on 100A cut out in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Got an EV (Nissan Townstar EV) in my house, has a Zappi EV charger installed (by myself) and notified via ENA form to Scottish Power energy...
Replies
4
Views
1K
Had UKPN come out to a property recently to upgrade the main fuse from 60A to 100A but when they arrived they said that the supply cable which he...
Replies
9
Views
2K
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
Hi there. I’m hoping for some advice. I currently run a small limited company that provides IT services, both commercial and domestic so I...
Replies
0
Views
647
Hi, Just had a new Smart Meter fitted yesterday along with isolator. The chaps installing the SMART meter used 16mm tails from the main DNO fuse...
Replies
16
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock