Hey all,

I have just finished a rewire of a 1 bed house and just have the board left to install. I am a qualified sparky but now work as a project manger so haven’t carried out much domestic work in the last couple of years. I know that the requirements for installing consumer units has now changed and am wondering what are the requirements with regard to cable entries into the board. I have the cables all dropping down from the ceiling where the existing board and meter position is in the entrance hall. Any advice would be appreciated.
 
Thanks for all the replies. Looks like back entry will be the best way to go.
On a side note I’ve seen online that suppliers are selling the semi blind grommets which it says are ip66 rated for use on cu’s. Would these comply with the new regs as I haven’t seen this method shown anywhere?

Cheers
The new Regs apply to the CU, not the cable entry points.
You only need IP4X/IPXXD on the top and IP2X/IPXXB on all the other sides.
Use IP66 grommets if you want, but there’s no requirement to do so.
 

Reply to 18th edition consumer unit in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top