Discuss 230V caravan installation in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
138
What documentation is required after wiring up a single phase installation in a caravan?
All mains testing has been done as if it were a domestic installation and tests out nicely.. I can do a domestic installation cert although the parts specifying the supply I feel are a bit superfluous as it could be from any applicable 230v supply, it's not fixed.
Also the requirements of section 721 have been adhered to.
Is a caravan classed as a Building? Does it need a Building Regs certificate?
I was going to enquire my assessor but judging from some of the comments I see on the forum, thought I'd ask here first..
 
EIC for provision of a new circuit or MWC for an alteration.

Record test results but state Ze/PFC etc only valid at time of test as caravan connected to temporary supply.
 
It's one of these..

1530397053322-1418723842.jpg
 
I think a domestic EIC, is for up to 100A supply?
Yes that's right I just checked..
And Murdoch is right too, there's no "official" domestic EIC, I just tend to call them that because that is what mainly I do.
There is similarly a Domestic Condition Report also for up to 100A..
Now we've cleared that up, perhaps we can get back to the questions on the OP? :)
 
EIC for provision of a new circuit or MWC for an alteration.

Record test results but state Ze/PFC etc only valid at time of test as caravan connected to the temporary supply it was connected to when the tests were done.

Corrected that for you

If you don't state that, then some numpty could assume the tests results would apply where ever the caravan was plugged in ........ which we all know won't be the case.

CYA
 
Corrected that for you

If you don't state that, then some numpty could assume the tests results would apply where ever the caravan was plugged in ........ which we all know won't be the case.

CYA
Well spotted, I had my beer goggles on...
 

Reply to 230V caravan installation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've been given a really interesting job to do, and that's to retrofit a vintage caravan with 230v. Another company is doing the renovation work...
Replies
7
Views
1K
We have started a business building garden rooms/caravans/mobile homes under the caravan act. We have only done one so far and I got an...
Replies
3
Views
1K
Hi, I've got to a point where I need to complete the EIC for the caravan I've been working on. This isn't a static caravan, so will be going from...
Replies
2
Views
1K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
962
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
529

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock