Discuss 2391 Past Paper with Answers (Part 2) in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

F

firemanowl

Here are questions 11 - 20, I have also found the long answer section with answers so will post shortly. I apologise if there are any mistakes but feel free to offer any corrections.

11 State the meaning of:

a) IP 2X
b) IP 4X
c) IP XXB (3 marks)

a) protection against a sphere of 12.5mm diameter by 80mm length.
b) Protection against a wire o1mm diameter (Standard Test Wire)
c) Protection against a ‘Standard Test Finger’ only.


12 State THREE areas within a construction site which are NOT subject to Part 7 of BS 7671:2008. (3 marks)

i) toilets
ii) mess rooms
iii) site offices.

13 List FOUR items of information that are required to be indicated on diagrams, charts etc., for use by the inspecting engineer. (3 marks)
i) type and composition of circuits
ii) method of protection against electric shock
iii) any circuit vulnerable to a particular test
iv) the identification and location of any device performing the functions of protection, isolation and switching.

14 State SIX methods of Fault Protection. (3 marks)i) Automatic Disconnection of Supply (ADS)
ii) Double or Reinforced Insulation (Class II)
iii) Non-Conducting Location
iv) Earth-Free Equipotential Bonding
v) Electrical Separation
vi) Extra Low Voltage (SEVV or PELV)
15 State:
a) the instrument used for a ‘dead’ polarity test
b) an instrument that may be used for a ‘live; polarity test
c) why certain E14 & E27 Edison screw lampholders do not require to be checked for polarity. (3 marks)

a) Low Resistance D.C. Ohmmeter
b) GS.38 Voltage Indicator testing between Live and Earth
c) Certain E14 & E27 lampholders have a non-metallic ‘screw’ insert. Contact with the lamp itself is made in the base of the fitting therefore not creating a risk of electric shock to a person inserting the lamp who may be touching the metal screw of the lamp.

16 State the units of measurement that are displayed on the following test instruments:
a) low resistance ohmmeter
b) insulation resistance tester
c) prospective fault current tester. (3 marks)

a) Ohms (Ω)
b) Mega Ohms (MΩ)
c) Kilo Amps (kA)
17 A continuity test between P and N is conducted on a ring final circuit comprising 2.5 mm[SUP]2[/SUP]/1.5mm[SUP]2 [/SUP]thermoplastic (pvc/pvc) cable. Readings at two socket outlets close to each other indicate an increased value to that of all the other sockets. State:
a) the instrument used for the test
b) TWO possible reasons for the increased readings. (3 marks)

a) A Low Resistance D.C. Ohmmeter.
b) i) The socket is a spur from another socket.
ii) There is a unacceptable bridge or interconnection in the ring final circuit.

18 Identify the type of circuit that would require the following applied voltages when conducting an insulation resistance test
a) 250 V dc
b) 500 V dc
c) 1000 V dc (3 marks)

a) An Extra-Low Voltage circuit (SELV or PELV).
b) Low Voltage up to 500 volts.
c) Circuit above 500 volts.

19 BS 7671:2008 requires that the ‘live’ polarity is verified before installation circuits are energised. State:
a) Why the live polarity test is needed
b) at what part of the installation the test would normally be made
c) ONE method of carrying out the test. (3 marks)

a) To confirm that the Supply Authority’s Polarity is indeed correct.
b) At the Origin.
c) Using a GS 38 approved Voltage Indicator and testing between the incoming Line and Earth conductors.

20 State three methods of ascertaining the value of prospective short circuit current at the origin of a TN-C-S system.
(3 marks)
Measurement, Enquiry or Calculation.
 

Reply to 2391 Past Paper with Answers (Part 2) in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
661
Hi I'm currently doing C&G 2365 Level 3 I'm working through the 305 design assignment (Swimming pool, hotel etc.) Other then this assignment I...
Replies
4
Views
4K
All - Would appreciate some advise or professional help as I'm facing a £4.5K bill following an EICR which seems to highlight issues that passed...
Replies
21
Views
4K
I've started to move over to AMD 2 forms for my CU installs, if only because the schedule is so much easier to tick and I can stop sticking labels...
Replies
4
Views
1K
So having a look at the electricians guide to the building regulations, section 7 safe working. 7.3 is about pre work tests and is states that...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock