on street lighting circuits we had problems when running anymore than 6 no400w son t fittings if one went faulty it would take out the mcb rather than the fuse in the fitting due to the additional fault time req for fuse against mcb
ie 400wx1.8 /230v = 3.14a per fitting 5 per curcuit =15.6a each fused @ 10A the mcb trips taking them all out as nick says
Mogga, I've change the configuration to utilise C rated MCB's, also reduced the lights to 9 x 250w per contactor which would now be 3 pole. Thats 3 lights on a radial per pole of contactor. The 3 light radial 250wx1.8/230v=1.95a - 3 fittings per circuit=5.86A.
I take your point - you reckon I should up the whole supply?? ie 60amp feed, C30 MCB to 30A contactor to C10 MCB's to lights??