Currently reading:
3 phase motor dropping voltage with load.

Discuss 3 phase motor dropping voltage with load. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
I have a 10 HP -230 volt 3 phase hydraulic press brake. I just installed a new 40 HP rotary converter panel with used WEG motor. The problem i am having is the volts going into the press during a load is dropping from 245 to 195-200 volt. Which means i'm loosing power of the hydraulic system. Wonder if anyone has a idea of what could be causing this. The required rotary converter is a 30HP and i went to a 40HP just to make sure.

I attacked pictures of the 40 HP used motor running my phase converter
 

Attachments

  • 162183-weg-cc0294-040360t3e286ts-40hp-electric-motor-208-460v-3ph-286tc-frame-3535-rpm-2.jpg
    129.8 KB · Views: 17
  • 162183-weg-cc0294-040360t3e286ts-40hp-electric-motor-208-460v-3ph-286tc-frame-3535-rpm-3.jpg
    112.9 KB · Views: 17
Agree with Pete, I would first check the supply to the converter, to see how much the voltage on the single-phase side is dropping. If that is reasonably steady, then check whether the voltage drop at the converter 3-phase output is symmetrical or not and perhaps report your findings to the panel manufacturers.

From what I can read on the plate the converter looks like a 12-wire motor. Is it definitely connected to the panel correctly, with the right voltage configuration? If the series-parallel arrangement of the windings is wrong, it might start and run OK but lack power as a converter once under load.
 
I have a 10 HP -230 volt 3 phase hydraulic press brake. I just installed a new 40 HP rotary converter panel with used WEG motor. The problem i am having is the volts going into the press during a load is dropping from 245 to 195-200 volt. Which means i'm loosing power of the hydraulic system. Wonder if anyone has a idea of what could be causing this. The required rotary converter is a 30HP and i went to a 40HP just to make sure.

I attacked pictures of the 40 HP used motor running my phase converter
Let me ask you a few questions when you changed from a 10 HP to a 40 HP did you up grade the starter size, the overloads, and the wiring. The starter should be size 4 and the wiring should # 8
Agree with Pete, I would first check the supply to the converter, to see how much the voltage on the single-phase side is dropping. If that is reasonably steady, then check whether the voltage drop at the converter 3-phase output is symmetrical or not and perhaps report your findings to the panel manufacturers.

From what I can read on the plate the converter looks like a 12-wire motor. Is it definitely connected to the panel correctly, with the right voltage configuration? If the series-parallel arrangement of the windings is wrong, it might start and run OK but lack power as a converter once under load.
I meant the starter size should be 3 not 4
 
Let me ask you a few questions when you changed from a 10 HP to a 40 HP did you up grade the starter size, the overloads, and the wiring. The starter should be size 4 and the wiring should # 8
I meant the starter size should be 3 not 4
Yes the starter has been upgraded. I bought a new starter panel from a rotary phase company. The wires run to everything has also been upgraded and is sized for 100 amp load. The motor is a 12 wire and i wired it to run 230 volt. It is a used motor.

this link is the 40HP panel i got to run everything. Very nice systems. I had a 20hp for years.

 
Let me ask you a few questions when you changed from a 10 HP to a 40 HP did you up grade the starter size, the overloads, and the wiring. The starter should be size 4 and the wiring should # 8
I meant the starter size should be 3 not 4


Also i didn't replace the 10hp on the press with a 40HP. The 40HP motor is what is running the 3 phase converter. Just wanted to make sure i said that correctly.
 
I have a 10 HP -230 volt 3 phase hydraulic press brake. I just installed a new 40 HP rotary converter panel with used WEG motor. The problem i am having is the volts going into the press during a load is dropping from 245 to 195-200 volt. Which means i'm loosing power of the hydraulic system. Wonder if anyone has a idea of what could be causing this. The required rotary converter is a 30HP and i went to a 40HP just to make sure.

I attacked pictures of the 40 HP used motor running my phase converter

I have a 10 HP -230 volt 3 phase hydraulic press brake. I just installed a new 40 HP rotary converter panel with used WEG motor. The problem i am having is the volts going into the press during a load is dropping from 245 to 195-200 volt. Which means i'm loosing power of the hydraulic system. Wonder if anyone has a idea of what could be causing this. The required rotary converter is a 30HP and i went to a 40HP just to make sure.

I attacked pictures of the 40 HP used motor running my phase converter
Hi you may have to check the following. loose wiring connections, defective circuit breakers, the contactor contacts may be pitted, mechanical defects.
 

Reply to 3 phase motor dropping voltage with load. in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top