3 phase volt drop calcs

Discuss 3 phase volt drop calcs in the UK Electrical Forum area at ElectriciansForums.net

W

wade88

Hi guys,

Looked over some previous posts and done some further reading, and attempted the calcs, just want to check that i am not miles off the ball park here with this. From what i have read harmonics and current down the neutral will cause massive fluctuations in results not to mention unbalanced phases but i would just like to get a broad figure so i have reference.

Cable run is 50 meters, 4 core SWA 25mm, clipped direct, 105 amps per phase.

Calculation i have been going on is:

mV/A/m x length x load / 1000 to find the approximate single phase volt drop in this circuit

and then multiply by 0.866 to take account for any current in the neutral

so im getting:

1.5 x 50 x 105/1000 = 7.875 x 0.866 = 6.81Volts.

Any one free to confirm they get similar results. Or have i missed an important part of the 3 phase calc process here.

Thanks guys


 
Or should it be 2.5 x 50 x 105/1000 x 0.866 = 11.36V

Cant decipher accurately what the mV is from the tables i have. Two tables are providing two different data sets but are titled the same? So not positive on which figure i should be using.
 
Hi Wade88,
According to the IEE design guide the formula (mV/A/m)z x L x Ib /1000 should be used, ie, the z value of 1.5mV/A/m if the power factor of the load is not known. As above:smilewinkgrin:
 
Just read your post...it should be single phase (2 core) volt drop times by square route of 3 divided by 2 (0.866) will give the 3 or 4 core volt drop in mV/A/m....
So it would be in your case single phase volt drop of 1.75 x 0.866 = 1.5mV/A/m
 
Last edited by a moderator:
lol oh thanks Tony....ill just jot that down on my lunch box for next time :ihih:

Yea 1.5 is what i had to begin with, so im happy with my results after that.

Thanks fellas.

I wish you all a great Christmas and a boozy new year.

Ben
 

Reply to 3 phase volt drop calcs in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock