We will have to agree to disagree on that but I hold your position to be questionable.
Running three single phase lighting circuits in one location to load spread is indeed common practice, but the only time they should be on a common 3P+N MCB/Isolator etc is when contractor controlled so they are effectively a 3 phase circuit and should be treated as such. Neutrals should not be looped though and may come back to a common point but should be separate for each on the lighting legs.
If you are talking about standard lighting circuits with conventional switching etc then they should be on separate MCB's and not a 3 pole. They should not have shared neutrals and to do so would be extremely bad in my humble opinion.
Oh by the way, just got off the Phone with the NICEIC who agree with me on this, as do NAPIT and ELECSA. I have also conferred with the IET who have condemned the notion of running single phase circuits, except as stated where controlled via a contactor, via a 3 pole MCB/Isolator whether the neutral is shared or not.
I will admit that no-one could specifically point to a regulation to prevent someone doing this, but all stated they would not consider this good practice or good design.