Discuss 3rd ring from garage in the DIY Electrical Advice area at ElectriciansForums.net

jonnachie

DIY
Reaction score
0
I have supply in the garage with its own small consumer unit with a 63a breaker and 1 B6 and 1 B16 breakers. The garage has a ring of sockets coming from the B16 breaker. An electrician has added a wire into the 16amp breaker to a second shed. So that is 2 rings from one B16 breaker. I now have a third shed. Can I put a third wire into the 16amp breaker or do I need to get a whole new consumer unit with 3, 16amp breakers, one for each shed? Thanks
 
It won’t be a ring…. As it’s only one cable, it’ll be a radial.

So at the moment you have 2 radial circuits from one 16A breaker. Perfectly within regulations.

The second shed can also come from this breaker, or be linked from the first shed… or from any socket in the garage from that 16A breaker.

These sockets must have rcd protection if there isn’t already.
 
It won’t be a ring…. As it’s only one cable, it’ll be a radial.

So at the moment you have 2 radial circuits from one 16A breaker. Perfectly within regulations.

The second shed can also come from this breaker, or be linked from the first shed… or from any socket in the garage from that 16A breaker.

These sockets must have rcd protection if there isn’t already.
Thanks Little spark
 

Reply to 3rd ring from garage in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I may have posted this before but not sure if it made it in. I want to install an EV Charger in my garage. The panel is two stories up and the...
Replies
0
Views
489
Hi I have a Corby 7700 trouser press it is a 220w model, 3 years 10 month old. On Friday it stopped working, so I took it to the garage ready...
Replies
1
Views
659
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
0
Views
596
Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
745
Background Two weeks ago, lightning struck a tree in our yard. Many circuits tripped and several electronic devices failed. There was a strong...
Replies
2
Views
866

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock