Search the forum,

Discuss 63 amp socket Table 41.1 in the UK Electrical Forum area at ElectriciansForums.net

Cookie

-
Reaction score
118
Does anyone know why 0.4 seconds was extended to 63 amp socket circuits? Is this because supply sources are getting stronger?

1616624338906.png
 
I think they are trying to bring protection for 63A sockets in line with the requirements for socket outlets of lower current ratings. Same with the RCD requirements changing.

Unless there's another reason anyone else is aware of.
 
In my world there's lots of things that are a final circuit (device) on a 63A ceeform, both 1ph and 3ph, so in that sense it makes, er, sense. But then that exact same cable can plug into and power a submain (rubber box distro's) and become a 5s circuit, so it's all about having a thought-through approach.
 
Danger is more for plugged devices due to the flex used.

Fixed loads are usually installed via flexi conduit, armoured cable or similar heavy duty cables.

Plugged in devices usually end up with fairly unprotected trailing leads.


I guess that means added impedance increasing disconnection times?
 
I guess that means added impedance increasing disconnection times?
No,

Likelihood of damage to cables.

Rcd are for the protection of persons, not equipment.

Trailing leads, associated generally with plugged in equipment tend to get damaged exposing cores, or potential short circuits.

An example may be a 63A welding set, loads of steel plate being moved around, and potential for dropping plate sharp edge-on to the welder supply cable.

Fixed equipment tends not to be like this.
 

Reply to 63 amp socket Table 41.1 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I’m testing some electric meters. As the circuits have no load on them to prove each ct I’ve plugged a hair dryer to simulate a load and...
Replies
3
Views
480
Hi, firstly appologies if my terminology is wrong but I know very little about electrics and have no idea why this is happening - I have 2...
Replies
4
Views
463
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
718
Hi everyone. I am really puzzled by this, but I suppose there is an obvious answer / reason! Anyway, Table I1 in the OSG says the mΩ/m value for...
Replies
2
Views
750
One of our contractors has identified a concern with multiple showers on a single 100 amp supply.(unsure how many yet i have asked for further...
Replies
3
Views
231

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top