so hager 16A 60898 type B will disconnect in 0.01s at 719A. Is this correct?
Yes, see attached pdf.
So with this I could go 2.5mm2 + 1mm2. r1+r2 = 0.21
Zs = .11 + .21 = .32
pfc = 230/.32 = 719A

so square root of 719 squared x 0.01/115 = 0.62 = S
The calculation looks right. Is the value of R1+R2=0.21 correct? It was 0.22 in your OP.

As before, I'd have used the fault current from the origin (2091A) for the calc, but I think this is something you'll have to ask your tutor, to confirm what he/she is expecting.

FWIW, I discussed this with a fellow spark's apprentice a while back (generally, not related to any specific question he had). Prompted by me, next time he was at college, he posed the question to his tutor: where in the circuit should the fault current be taken from when calculating the adiabatic, for these types of breaker? His tutor admitted he didn't know.
 

Attachments

  • hager curve.pdf
    90.9 KB · Views: 11
Yes, see attached pdf.

The calculation looks right. Is the value of R1+R2=0.21 correct? It was 0.22 in your OP.

As before, I'd have used the fault current from the origin (2091A) for the calc, but I think this is something you'll have to ask your tutor, to confirm what he/she is expecting.

FWIW, I discussed this with a fellow spark's apprentice a while back (generally, not related to any specific question he had). Prompted by me, next time he was at college, he posed the question to his tutor: where in the circuit should the fault current be taken from when calculating the adiabatic, for these types of breaker? His tutor admitted he didn't know.
I made a mistake with the initial post. r1+r2 was supposed to be .12, with 2.5mm2 + 2.5mm2.
I've calculated the r1+r2 now using 2.5mm2 + 1mm2.

One last question hopefully... in the pdf you posted why does the line stop at 4 and 6 where as the type c graph the line continues upto 100?

My fault current would be at the 44 mark i think... 719/16 = 44.9 as timhoward said above?

I know this is a lot of questions however I have actually got a much better grasp on this now so thankyou all!!
 
I made a mistake with the initial post. r1+r2 was supposed to be .12, with 2.5mm2 + 2.5mm2.
I've calculated the r1+r2 now using 2.5mm2 + 1mm2.

One last question hopefully... in the pdf you posted why does the line stop at 4 and 6 where as the type c graph the line continues upto 100?

My fault current would be at the 44 mark i think... 719/16 = 44.9 as timhoward said above?

I know this is a lot of questions however I have actually got a much better grasp on this now so thankyou all!!
The missing line on the pdf for b-curve is just a printing error. For all 3 curves, once a threshold current is exceeded, the breaker is not expected to operate any faster than 0.01 seconds.

Another small detail, but important: r1, rn, and r2 (lower case 'r') are the resistances of the conductors of a ring final, measured end-to-end. I assume in this case you're dealing with a radial circuit? for which you should use R1, Rn, and R2 (capital 'R') to indicate the conductor resistances.
 
The basic steps are usually easy to follow, but the 't' in your I2t formulae is the one that usually catches folks out as the curves in the regs only go down to 0.1s even though standard energy-limiting breakers operate in less than a cycle of the supply (so below 20ms).

Another oddity is once you get down much below 0.1s there is the issue of where in a cycle of the AC a fault occurs and what that means. Fortunately that answer is "very little" as energy limiting devices like MCB and fuses react to a degree to the fault energy and so laraely compensate for phase of fault occurrence. The axis of time is what is known as "virtual time" since it relates directly to the resulting I2t let-through.

TL;DR the time values are their precisely to compute I2t

So for some fuses (see below) you will see the time axis go down to 0.0001 seconds = 0.1ms = 100us but that does not mean they open in microseconds, what is happening is the fuse is current-limiting as the internal wire arcs so the fault clearing might be a couple of milliseconds but the I2t value is far less (as limited current is below the PFC) but if you use the PFC and virtual time values you get the right answer.
10x38-fuse-time-curves.png
MCB also provide some limitation but unlike fuses they don't limit nearly as well, even though the I2t immediately in the "instant" magnetic region is less then the equivalent fuse. Breakers have a mechanical opening time that speeds up a bit as PFC rises, but not nearly as quickly as the I2t rises, hence the typical shape shown in the Hager graph in post #4 of this thread.
 
@timhoward , I believe that, for B and C type breakers, the fault current used for the adiabatic equation should be taken at the point of the circuit that it would be highest, ie the origin. The reasons for this are in my above post, also the note to fig3A4 ('The application of the rules of Chapter 43 should take into account both minimum and maximum fault current conditions.').

To me, it seems that using the fault current at the far end of the circuit leads to a CPC being selected on a best case scenario, and a fault anywhere else in the circuit would raise the temperature of the conductors to a higher temperature than a fault here would.

I raised this question with my tutor as an apprentice and was told that as the fault current is higher the speed of operation of the device will be faster at the origin.
As the device operates faster the temperature rise will be less, and not more, than at the end of the circuit.
Therfore we calculate based on the PFC at the end of the circuit as it will automatically comply at the origin if it complies at the end, but not necessarily the other way round.
 
I raised this question with my tutor as an apprentice and was told that as the fault current is higher the speed of operation of the device will be faster at the origin.
As the device operates faster the temperature rise will be less, and not more, than at the end of the circuit.
For a fuse that is true as PFC rises the time decreases at a much higher rate (I^[3..4] sort of speed) so overall I2t drops.

However, for breakers that is not the case. While the equivalent disconnection time still drops it is not fast enough to compensate for the square-law of the I2 current factor rising.
 

Reply to Adiabatic Equation help in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
800
Hi Help please with the adiabatic I am doing a small design for my course and I can't figure it out. Any advice will be appreciated. Ring Final...
Replies
15
Views
2K
Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...
Replies
13
Views
3K
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Replies
4
Views
3K
Hi All, I think I have confused myself somehow and feel I am spiraling into further confusion. When I am doing the equation, it is saying the...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock