Ok I get called to a job where there is no power to the flat. Intake is in a small basement cupboard, 25mm swa protected by a Bs88 80a fuse in a switch fuse. Test for continuity and the fuse has blown. Fit a new one and I'm sure you can guess the outcome..... New fuse blows.
Go up the the tenants cu and ir at 250v the incoming swa tails, live to neutral, live to earth etc and get a reading of around 150mohms on each. Now This job was last thing tonight and my brain is frazzled, what am I missing, the cu is a 16th edition skeleton board, around 15 years old, no one else is affected in the flats, oh and the new fuse blew with the main switch off
 
Do you make a habit of changing fuses without testing first... Id have been inclined to at least switch D.B. off and test the supply cable before replacing a blown fuse... then confirmed the circuits before energising if supply cable tested fine.

A bit arris about face your methods Pondy but I'm sure you'll do the correct sequence next time ;)
 
Since you tested after replacing the fuse and not before I would suggest that the fault has blown itself apart when the new fuse was put in.
It is always sensible to tests before replacing a blown fuse, especially when larger fuses are concerned.
 
On seeing a fuse of that size blown,more than a cursory glance would be necessary before jamming another round up the breach and shooting off in to the dark. :stooge_curly:
 
Agreed a spot of testing wouldn't of gone amiss, but I was parked in the road in a permit area and had one eye out for the traffic warden, the cu main switch was off darkwood,surely insolation resistance of the tails from the main switch back would of found an issue
 
The you should have parked more sensibly! What if the arc at the fault when you applied power had started a fire? Would you stand up in court and use your poor parking as an excuse for burning down a house?

Insulation resistance testing could have found a fault before you put the fuse in, but if the fault blew itself apart when the fuse was put in it won't now will it?
 
Adam, sorry yes I do mean mega ohms, dave sparks it wasn't poor parking and I wasn't making excuses, all the pay and display was full and there nearest was quarter of a mile away, and a permit space in the road outside the job was empty.
I don't understand quite what you mean, surely the fault is still there and as such should be traceable
 
I think what he's getting at is that with the power being put back on it's literally blown the fault clear. However what will be glaringly obvious now is something not working but with your main switch off it would point to a supply issue
 
You can blow a fault clear. But it’s usually due to damp. The heat of the flashover dries the fault out.

I spent nearly a month looking a UG cable fault. Every time the fuses blew it would test perfect afterwards. Finally found it by putting copper links in place of the 450A fuses. The ground erupted and a tree fell over, gave the game away really. The tree roots had disturbed a through joint and damp was getting in.
 
What’s wrong with the “bang” test? Some people are just too fussy.

Only worth it if you have spare fuses or reset devices and a risky nature ;)

What kind of tree was it Tony ..possible an amPEAR tree


Already getting my coat:89:
 
Adam, sorry yes I do mean mega ohms, dave sparks it wasn't poor parking and I wasn't making excuses, all the pay and display was full and there nearest was quarter of a mile away, and a permit space in the road outside the job was empty.
I don't understand quite what you mean, surely the fault is still there and as such should be traceable

For example if there was a short in an SWA cable where say a screw had penetrated it and made a connection between the armour and live then a large current will have flowed through the screw before the fuse operated. This fault current often manifests itself as a loud, bright discharge of energy which can dislodge the screw, melt through it or melt through the copper of the cable. Any of these things happening will remove the short circuit but obviously leave the cable significantly damaged.
 
That part I don't get, is surely if I've meggered from the cu live and neutral. Live to earth etc that proves that there is no fault with the swa as the insolation resistance is fine, but the fuse is still blowing
 
Did you test to the armour as well (assuming this is not used as the earth!) and is the armour properly terminated at both ends.
It may be possible to have a line to armour fault and the armour not earthed at the CU end only the supply end.

EDIT: or perhaps an internal short inside the switch fuse before the switch
Is there a landlords CU that actually has the fault on it that is connected to the same supply cable?
 
That part I don't get, is surely if I've meggered from the cu live and neutral. Live to earth etc that proves that there is no fault with the swa as the insolation resistance is fine, but the fuse is still blowing


This is why you ''NEVER'' replace a blown fuse (of unknown cause) ''BEFORE'' conducting tests to confirm that no fault is present. Your statement above about everything is now fine could well be wishful thinking on your part, significant damage to the cable or other components could well exist, just waiting to cause even more problems later!!
 
E54, yes I know I should of done, Richard thanks for your input, I know the armour is not used as an earth, it has a separate earth, just can't see how there is a problem still and its not showing up
 
What's the I.R from the Switch fuse end?

What's the route of the cable, does it pass thro' another flat?
Is there any work being done anywhere in the building?
 
E54, yes I know I should of done, Richard thanks for your input, I know the armour is not used as an earth, it has a separate earth, just can't see how there is a problem still and its not showing up

There may be damage to the cable (or other components) that through blowing itself clear won't show any or little sign of the damage. For instance, a 16 mm conductor could have been reduced to 6mm or less by the discharge of energy clearing the fault.... Now what can you see potentially happening when that cable is loaded up for any period of time??

That's just one situation, and perhaps the easiest to describe and envisage, but there are also other reasons.
 
When you say theres a separate earth , it could be the armour is not earthed at all i.e. plastic enclosures maybe and the clear reading to earth is not via the armour but the separate earth. have you tested to the armour ??


Another thought if it goes through someone else's flat , could be someone has been messing with it for a cheap leccy supply , you never know ...
 
Last edited by a moderator:
Ok I get called to a job where there is no power to the flat. Intake is in a small basement cupboard, 25mm swa protected by a Bs88 80a fuse in a switch fuse. Test for continuity and the fuse has blown. Fit a new one and I'm sure you can guess the outcome..... New fuse blows.
Go up the the tenants cu and ir at 250v the incoming swa tails, live to neutral, live to earth etc and get a reading of around 150mohms on each. Now This job was last thing tonight and my brain is frazzled, what am I missing, the cu is a 16th edition skeleton board, around 15 years old, no one else is affected in the flats, oh and the new fuse blew with the main switch off
Crickey, really?
 
this highlights the advantages of the good old Drummond test lamp,you made sure the load end was isolated and put the lamp across the fuse carrier,if the lamp lit you knew there was a fault and didn't put the fuse in.
 
Agreed a spot of testing wouldn't of gone amiss, but I was parked in the road in a permit area and had one eye out for the traffic warden, the cu main switch was off darkwood,surely insolation resistance of the tails from the main switch back would of found an issue

Traffic wardens can be a hazard of the job but testing is a must , what you should do is disconnect both ends of the cable insulate the bare ends at the opposite end where your testing from and then test from one end this way your less likley to zap the curious customer could be mr DIY put a nail through the cable ,no sign of any smoking trainers any where
 
Fuses don't blow without reason, short circuit, or over load current.
There is nothing in this life that happens without a reason,metaphysical discussions apart...unless your my 6 year old,in which case,it genuinely,"...just happened..." :smilewinkgrin:
 
You can blow a fault clear. But it’s usually due to damp. The heat of the flashover dries the fault out.

I spent nearly a month looking a UG cable fault. Every time the fuses blew it would test perfect afterwards. Finally found it by putting copper links in place of the 450A fuses. The ground erupted and a tree fell over, gave the game away really. The tree roots had disturbed a through joint and damp was getting in.
yep....
i remember you telling me about that breeched paper-lead on the phone the other week...
 
Ok I get called to a job where there is no power to the flat. Intake is in a small basement cupboard, 25mm swa protected by a Bs88 80a fuse in a switch fuse. Test for continuity and the fuse has blown. Fit a new one and I'm sure you can guess the outcome..... New fuse blows.
Go up the the tenants cu and ir at 250v the incoming swa tails, live to neutral, live to earth etc and get a reading of around 150mohms on each. Now This job was last thing tonight and my brain is frazzled, what am I missing, the cu is a 16th edition skeleton board, around 15 years old, no one else is affected in the flats, oh and the new fuse blew with the main switch off
so..
is it a 3 core SWA?
and if so i take it you tested the cores to the armourings as well then?...
 
Would like to thank everyone who has responded to this post in a helpful manner, I'm on this forum a lot and don't often post answers as I'm afraid of putting up incorrect information, I suppose a lack of confidence.
E54 especially I would like to thank for drawing my attention to a couple of things I hadn't thought of. we are all human and make mistakes and sometimes cut corners, it's not right, just saying. I would not like to thank mdj, I thought post 26 was unnecessary, ****ty and superior. If you can't post anything helpful then don't. Rant over, tin hat on. Thanks guys
 
Would like to thank everyone who has responded to this post in a helpful manner, I'm on this forum a lot and don't often post answers as I'm afraid of putting up incorrect information, I suppose a lack of confidence.
E54 especially I would like to thank for drawing my attention to a couple of things I hadn't thought of. we are all human and make mistakes and sometimes cut corners, it's not right, just saying. I would not like to thank mdj, I thought post 26 was unnecessary, ****ty and superior. If you can't post anything helpful then don't. Rant over, tin hat on. Thanks guys
Sorry I offended you, I meant well, I do feel a qualified electrician could get to the bottom of the problem with the correct test equipment quite quickly and cheeply, sorry again.
 
Ponds lighten up every one on here takes the p (well not every one ) but if they do you will learn and not forget the answers to the problem
So making you a better cowboy ( you did say you cut corners )
I was joking
And mdj deep down is a loving caring helpful person

Bloody deep down though
I can't get the little pictures up though sorry
 
Apology accepted, constructive criticism I can take, apologies to the mods for the swear word, I'd had a couple of beers and it just popped in. :)
 
And 5 days on it doesn't sound like its sorted. Lets hope the electric shower etc isn't on in the flat for too long :s
 

Reply to Am I missing something here in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Just had a phone call from an existing customer. He has just had solar panels put in, along with a very large battery. He has a single up front...
Replies
12
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hello all First time relocating a DB and just want to clarify my plans and check if missing anything. I have attached a photo of current DB and...
Replies
15
Views
1K
Evening All, I attended a job today to disconnect an Alarm System at a ground floor flat. On taking the consumer unit front off, discovered the...
Replies
29
Views
4K
Thought I'd seek some advice on something has been frustrating, and the frustration may now be clouding judgement....! It was 30A rewirable fuse...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock