What's the I.R from the Switch fuse end?

What's the route of the cable, does it pass thro' another flat?
Is there any work being done anywhere in the building?
 
E54, yes I know I should of done, Richard thanks for your input, I know the armour is not used as an earth, it has a separate earth, just can't see how there is a problem still and its not showing up

There may be damage to the cable (or other components) that through blowing itself clear won't show any or little sign of the damage. For instance, a 16 mm conductor could have been reduced to 6mm or less by the discharge of energy clearing the fault.... Now what can you see potentially happening when that cable is loaded up for any period of time??

That's just one situation, and perhaps the easiest to describe and envisage, but there are also other reasons.
 
When you say theres a separate earth , it could be the armour is not earthed at all i.e. plastic enclosures maybe and the clear reading to earth is not via the armour but the separate earth. have you tested to the armour ??


Another thought if it goes through someone else's flat , could be someone has been messing with it for a cheap leccy supply , you never know ...
 
Last edited by a moderator:
Ok I get called to a job where there is no power to the flat. Intake is in a small basement cupboard, 25mm swa protected by a Bs88 80a fuse in a switch fuse. Test for continuity and the fuse has blown. Fit a new one and I'm sure you can guess the outcome..... New fuse blows.
Go up the the tenants cu and ir at 250v the incoming swa tails, live to neutral, live to earth etc and get a reading of around 150mohms on each. Now This job was last thing tonight and my brain is frazzled, what am I missing, the cu is a 16th edition skeleton board, around 15 years old, no one else is affected in the flats, oh and the new fuse blew with the main switch off
Crickey, really?
 
this highlights the advantages of the good old Drummond test lamp,you made sure the load end was isolated and put the lamp across the fuse carrier,if the lamp lit you knew there was a fault and didn't put the fuse in.
 
Agreed a spot of testing wouldn't of gone amiss, but I was parked in the road in a permit area and had one eye out for the traffic warden, the cu main switch was off darkwood,surely insolation resistance of the tails from the main switch back would of found an issue

Traffic wardens can be a hazard of the job but testing is a must , what you should do is disconnect both ends of the cable insulate the bare ends at the opposite end where your testing from and then test from one end this way your less likley to zap the curious customer could be mr DIY put a nail through the cable ,no sign of any smoking trainers any where
 
Fuses don't blow without reason, short circuit, or over load current.
There is nothing in this life that happens without a reason,metaphysical discussions apart...unless your my 6 year old,in which case,it genuinely,"...just happened..." :smilewinkgrin:
 
You can blow a fault clear. But it’s usually due to damp. The heat of the flashover dries the fault out.

I spent nearly a month looking a UG cable fault. Every time the fuses blew it would test perfect afterwards. Finally found it by putting copper links in place of the 450A fuses. The ground erupted and a tree fell over, gave the game away really. The tree roots had disturbed a through joint and damp was getting in.
yep....
i remember you telling me about that breeched paper-lead on the phone the other week...
 
Ok I get called to a job where there is no power to the flat. Intake is in a small basement cupboard, 25mm swa protected by a Bs88 80a fuse in a switch fuse. Test for continuity and the fuse has blown. Fit a new one and I'm sure you can guess the outcome..... New fuse blows.
Go up the the tenants cu and ir at 250v the incoming swa tails, live to neutral, live to earth etc and get a reading of around 150mohms on each. Now This job was last thing tonight and my brain is frazzled, what am I missing, the cu is a 16th edition skeleton board, around 15 years old, no one else is affected in the flats, oh and the new fuse blew with the main switch off
so..
is it a 3 core SWA?
and if so i take it you tested the cores to the armourings as well then?...
 
Would like to thank everyone who has responded to this post in a helpful manner, I'm on this forum a lot and don't often post answers as I'm afraid of putting up incorrect information, I suppose a lack of confidence.
E54 especially I would like to thank for drawing my attention to a couple of things I hadn't thought of. we are all human and make mistakes and sometimes cut corners, it's not right, just saying. I would not like to thank mdj, I thought post 26 was unnecessary, ****ty and superior. If you can't post anything helpful then don't. Rant over, tin hat on. Thanks guys
 
Would like to thank everyone who has responded to this post in a helpful manner, I'm on this forum a lot and don't often post answers as I'm afraid of putting up incorrect information, I suppose a lack of confidence.
E54 especially I would like to thank for drawing my attention to a couple of things I hadn't thought of. we are all human and make mistakes and sometimes cut corners, it's not right, just saying. I would not like to thank mdj, I thought post 26 was unnecessary, ****ty and superior. If you can't post anything helpful then don't. Rant over, tin hat on. Thanks guys
Sorry I offended you, I meant well, I do feel a qualified electrician could get to the bottom of the problem with the correct test equipment quite quickly and cheeply, sorry again.
 
Ponds lighten up every one on here takes the p (well not every one ) but if they do you will learn and not forget the answers to the problem
So making you a better cowboy ( you did say you cut corners )
I was joking
And mdj deep down is a loving caring helpful person

Bloody deep down though
I can't get the little pictures up though sorry
 
Apology accepted, constructive criticism I can take, apologies to the mods for the swear word, I'd had a couple of beers and it just popped in. :)
 

Reply to Am I missing something here in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock