Hi All,
I'm a newby to the forum & am hoping to get some help from other members that are 'au fait' with the 17th edition regulations &/or Amtech Power Software.
My problem relates to the errors received after designing a domestic board. The calculations are bringing up a requirement for 15kA rated CPD's so as to be greater than the calculated PSCC of approx. 13kA.
Why would the value of the PSCC be so high in this case for a TN system?
How is it possible to reduce the PSCC so that the use of standard 6kA or even 10kA rated CPD's could be employed?
I beleive that I have tried everything within the constraints of the software but to no avail, so far.
Any help would be appreciated.
Clayton
 
hi..

well employing ohms law to the problem..
assuming nominal voltage of 230v.. to return your calcualted pscc of 13KA
would be 230 divided by 13000 = 0.018 ohms

so to bring pscc down would require larger number for the resistance.

what numbers is the software using and where is it getting them from..?
 
Last edited by a moderator:
Hi bcm spark,
I bought the 16th Edition software in 2006 & received the new 17th Edition software last year. I think it initially cost our Company in the region of £1000.00 but to receive updates & the new software you have to pay a monthly fee for the PremierCare which was initially about £50.00 per month but is now around £65.00 per month.
For your information, I think the software is pretty powerful but have attended a couple of the day courses to hone my skills as we do not have an I.T department or anybody else within the Company who is able to use it!
I hope that this helps. :)
Clayton
 
GT1,
Thanks for your reply.
You inspired me to revisit the software & look at the options it gave me & the values I had inserted with relation to the supply. The only values I had not really played with was the REC Supply Fault Level Calculator, as there were only 2 items to change - the size & length of the supply cables. What I didnt realise is that the length needed to be to the Elec Board cut out switch (which wasnt really clear).
So increasing the length of the supply cable which in turn will increase the resistance therefore reducing the PSCC. I just need to know for sure where the REC cut out switch is!

Once again, Thanks :)

Clayton
 
ha...
your welcome.!
it was a bit of a stab in the dark to be honest, not knowing the software...
sometimes though another pair of eyes on the problem can help i guess.
good luck with the rest of it.
 

Reply to Amtech ProDesign Domestic 17th Edition in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top