This is my first post so Hello to everyone and what a great forum this is.
Just reading the practical guide to Inspection, Testing and Certification of Electrical installations by Christopher Kitcher. Seems a good book as I am going for my 2391 after Christmas so Iam just reading up ready. On page 174 there are some exercises to do and I am struggling to get the same answer as in the back. Heres the Question-
You have installed a new ring circuit consisting of eight socket outlets on the ground floor of a detached house for Mr Hawth who resides in Crawley, Hampshire
There is no documentation available for the existing installation, but it appears to be in good condition. There is space available in the existing consumer’s unit for a new circuit.
The supply is a TNCS 230V 50Hz single phase, with an 80amp supply fuse to BS1361. Measured value of PSCC and Ze are 1350A and 0.28Ώ, respectively. On completion of the additional work the maximum demand is 78 amps.
Meter tails are 16mm² copper, the earthing conductor is 10mm² copper, and the main equipotential bonding conductors to the oil and water supplies are 10mm² (correctly connected).
The new circuit is wired in 63metres of 2.5/1.5mm² thermoplastic PVC twin and earth cable. Protection is by a 30A BS 3036 semi enclosed rewirable fuse which has a maximum Zs value of 1.09Ώ. The consumer’s unit, situated in a cupboard in a hall, has a 100A BS EN 61008-1 RCD as a main switch with an I▲n rating of 30mA. It has a tripping of 56ms at its rating and 24ms at five times its rating. The insulation resistance value is >200MΏ
A visual inspection of the new circuit shows no defects,and the test instrument used is a Megger multifunction instrument, serial number CJK1047.
2. Complete the paper work
The spur is to be 2.5/1.5mm² twin and earth PVC. The resistance of the 2.5mm² is 7.41mΏ per metre and the resistance of the 1.5mm² is 12.1mΏ per metre
The books answer for R1+R2 on the spur is 0.28 but I cant seem to get that. The question seems a bit vage on correction factors etc.
Any help would be much appreciated,
Thanks
This is my first post so Hello to everyone and what a great forum this is.
Just reading the practical guide to Inspection, Testing and Certification of Electrical installations by Christopher Kitcher. Seems a good book as I am going for my 2391 after Christmas so Iam just reading up ready. On page 174 there are some exercises to do and I am struggling to get the same answer as in the back. Heres the Question-
You have installed a new ring circuit consisting of eight socket outlets on the ground floor of a detached house for Mr Hawth who resides in Crawley, Hampshire
There is no documentation available for the existing installation, but it appears to be in good condition. There is space available in the existing consumer’s unit for a new circuit.
The supply is a TNCS 230V 50Hz single phase, with an 80amp supply fuse to BS1361. Measured value of PSCC and Ze are 1350A and 0.28Ώ, respectively. On completion of the additional work the maximum demand is 78 amps.
Meter tails are 16mm² copper, the earthing conductor is 10mm² copper, and the main equipotential bonding conductors to the oil and water supplies are 10mm² (correctly connected).
The new circuit is wired in 63metres of 2.5/1.5mm² thermoplastic PVC twin and earth cable. Protection is by a 30A BS 3036 semi enclosed rewirable fuse which has a maximum Zs value of 1.09Ώ. The consumer’s unit, situated in a cupboard in a hall, has a 100A BS EN 61008-1 RCD as a main switch with an I▲n rating of 30mA. It has a tripping of 56ms at its rating and 24ms at five times its rating. The insulation resistance value is >200MΏ
A visual inspection of the new circuit shows no defects,and the test instrument used is a Megger multifunction instrument, serial number CJK1047.
- Complete the correct paper work.
2. Complete the paper work
The spur is to be 2.5/1.5mm² twin and earth PVC. The resistance of the 2.5mm² is 7.41mΏ per metre and the resistance of the 1.5mm² is 12.1mΏ per metre
The books answer for R1+R2 on the spur is 0.28 but I cant seem to get that. The question seems a bit vage on correction factors etc.
Any help would be much appreciated,
Thanks