Thanks for digging that out, to me it only shows the phase being coil controlled by the large coil on the back of the unit, the smaller wire coil and toroidal unit controlling the arc disconnection, by my estimation to be a truly dual pole breaker there would have to be two large coils controlling the phase and neutral independently, supposition on my part, but that's where I was coming from in my previous post when I posted that the unit needing to be two module in width, there have been lots of claims of dual RCBO's prior to this point, but as I posted above they need to separate the contacts by 3mm to conform to the EU standard, I certainly look forward to someone finding one, as I have run out of room in my CU.
[automerge]1597705509[/automerge]
Difficult to see the circuit diagram on the side of the FuseBox RTAMB, but it does look as though it is double switched, by one coil, would be interested in the separation gap of the contacts, I will try to contact them tomorrow.
[automerge]1597705509[/automerge]
Difficult to see the circuit diagram on the side of the FuseBox RTAMB, but it does look as though it is double switched, by one coil, would be interested in the separation gap of the contacts, I will try to contact them tomorrow.